Page 7 of Tesla Gen 3 listed instructions prohibit Eaton BR equipmentEaton is claiming they have never heard of this before, and at this point is not able to offer any reasoning or solution.
My clients set their Tesla dashboard to 24 Amps, which charges slowly overnightHe dialed the charger back to 80% as recommended by Eaton. After about 30 minutes of charging, a total of 10 breakers have tripped
It does not prohibit BR equipment. It is saying if you have a BR loadcenter with an aluminum buss you need to use a 22K breaker instead of a 10K breaker. That makes zero sense. I doubt the buss clip is different on 10K and 22K breakers.Page 7 of Tesla Gen 3 listed instructions prohibit Eaton BR equipment
WARNING: Do not use Eaton BR branch breakers for Universal Wall Connector when the Electrical Panelboard
is made of Aluminum. Recommend instead using Eaton BRH branch breakers.
My clients set their Tesla dashboard to 24 Amps, which charges slowly overnight
The installer’s job is to follow listed instructions, not ask why. 110.3(B)It does not prohibit BR equipment. It is saying if you have a BR loadcenter with an aluminum buss
New construction works better without occupancy.On new construction we always set the chargers on 60 amps (48 amp charge rate)
Please read this statement 10 times.The installer’s job is to follow listed instructions, not ask why. 110.3(B)
Tin-plated is still Aluminum, so BR will be prohibited, since Eaton no longer makes a copper bus for residential Panelboards.
This WARNING was added very recently.WARNING: Do not use Eaton BR branch breakers for Universal Wall Connector when the Electrical Panelboard is made of Aluminum. Recommend instead using Eaton BRH branch breakers.
Watch out for call backs, if BRH bolt on internals may be similar to BR plug on.It says not to use BR breakers in Loadcenters with AL bussing but BRH breakers are ok.
There is no such thing as a BRH bolt-in. A BRH is a 22K version of a standard BR plug-in breaker.Watch out for call backs, if BRH bolt on internals may be similar to BR plug on.
Almost seems like that has something to do with an instantaneous trip incident rather than a busbar/breaker overheating issue. But then, I'm trying to make it make sense, which might be unwarranted.There is no such thing as a BRH bolt-in. A BRH is a 22K version of a standard BR plug-in breaker.
copper bus after 
But the trip rating is the same on the BR and BRH. Just the case is stronger to contain the internal parts under a bolted fault. Would love to hear Tesla's reasoning.Almost seems like that has something to do with an instantaneous trip incident rather than a busbar/breaker overheating issue. But then, I'm trying to make it make sense, which might be unwarranted.
If Eaton BR is defective during continuous loads, there should be a recall...my boss has the same issue really upset customer, Eaton AFCI's tripping, Tesla charger, 5 year old panel he installed. ..1/2 hour, you could smell the panel cooking.
I was sent to replace the the panel to copper bus SQD QO.