Following most everyone's elses leads, charlieb gets the brass ring (post 13): 60V Line C to Neutral
Requires balance 3ph load. Note 1ph loads connected line to neutral need not be balanced. They don't change anything.
The load between B and C is in series with the load between C and A. Since they are balanced, each load has 104V across it. But the mid-point, C, is elevated 60V, 104/(sqrt(3)), So, "none of the above".
This is not true if the 3ph loading is motor loads. Dropping a phase to motor loads, the voltage on the dropped phase really looks screwy. Could even read normal.
But the answer could also be "zero", if it is all single phase L-N loads or no loads at all
I think everyone is correct - very poor question.
This is one of those where I get my answer marked wrong, challenge the instructor. pointing out my assunmptions and that the test writer's assumptions are no more valid - it is a poor question. Instructor :rant: gets red in the face, tells me he is the writer and his answer is right and I :dunce: got it wrong. The conversation deteriorates further. :slaphead: Which is odd, cause I thought it had deteriorated about as far as it could.
and now I am known as
The Worm :angel: