Not necessarilly. A high resistance ground fault, as this appears to be, would not allow the current to get into the mag trip range. On a 15A CB, the mag trip setting could be anywhere from 6-10x the thermal rating, so that's 90-150A. If the resistance on the ground fault was keeping it at 65A, I would not expect the mag trips to activate.
And by the way, an IEC breaker would be no different... Their trip curves, both thermal and magnetic, are basically the same as ours for residential installations. They do offer more choices in mag trips that can accommodate things like motor and transformer inrush, but that's not typically what gets installed in houses. On the other side of this is the fact that their GF breakers allow 30mA of current for human contact, we only allow 6mA. We call 30mA "Equipment Ground Fault" protection, not personnel protection. I'll take ours, thank you...