The breakers BigJohn put under over current test were not the red handle breakers.
Pretty sure they were, that was the point of his testing but I won't argue the point because I am not sure of it.
The breakers BigJohn put under over current test were not the red handle breakers.
Pretty sure they were, that was the point of his testing but I won't argue the point because I am not sure of it.
Oh, ok, got it. So you put the amp clamp on the conductor and then turned the breaker on.
And the home owner told you it took some time to trip. But why do you think new breakers will hold 65amps for for some time?
And the home owner told you it took some time to trip. But why do you think new breakers will hold 65amps for for some time?
Yes, wouldn't an electrician know this?.
Because they will?
I have watched a Square D QB single pole 30 carry over a 130 amps for at least 5 seconds until a micro switch in the circuit gave out.
Which, if compared to its time current curve is 100% acceptable.
Yes, you are right Peter D never made that claim, but the part which puzzles me is when he compared FPE breakers to new ones. New breakers are light years ahead in reliability and being within factor specd trip curves.
Yes, wouldn't an electrician know this?![]()
I'm assuming a QO or Homeline would likely trip instantly, a GE might buzz for a few seconds then trip, a CH BR or Siemens would probably trip instantly too. Point being, the FPE is obviously living up to its reputation.
That's the point of this whole thread, to highlight how bad FPE is. I don't see much FPE in my area and I'm in and out of houses every day. It's even more rare that I actually get to see a fault on an FPE breaker.
Which, if compared to its time current curve is 100% acceptable.
.
New breakers are light years ahead in reliability and being within factor specd trip curves.
Which you believe from reading which makes you much like BPH. Not living in the real world.
Yet it happened and it is not FPE.
I tend to turn the circuit on and then amp clamp it. But thats because I have to much faith in newer breakers :lol:
Well, to be honest even a QO would take up to 20 seconds to trip for a 20amp version. Yes QO has the lowest magnetic trip of any breaker, but 65 amps is not approaching the value. So I disagree that FPE is living up to its name if you did not give the breaker more then 30 seconds to hold.
In so far, other then what the customer told you, nothing supports the idea the breaker you reset is defective.
I don't know that the breaker is defective, but since it's an FPE it is junk and should be replaced. I'm not an expert on current/time graphs but I'm used to instantaneous tripping with a dead short in a residential setting (short branch circuit length, relatively low impedance.) Just a cautionary tale about FPE, don't read into more than what I have said.
I don't know that the breaker is defective, but since it's an FPE it is junk and should be replaced.
At the very least they are old and should be replaced based on their poor 'stab loc' connection to the bus bar.
65 amps is not a dead short, at least with the impedance and available fault current in new wiring. Either way 65 amps will not trip any new breaker immediately, even a 16 amp IEC breaker. A 6 amp type B IEC breaker will however.
Im not saying this to make you feel bad or anything, but I just want to add my 2 cents to this. BTW, you are on to something big :happyyes:![]()
Well, you seem to know more about this job and I didn't happen to see you there the other day. :roll:
Im going by what you have said thus far.
1. You amp probed the breaker
2. you turned it on, 65 amps, and then shut it off a few seconds latter
3. You claim a new breaker would have tripped faster so thus FPE is bad. (though I do not dispute FPE being bad)
In reality time current curves show that a 15 amp breaker can hold 65 amps for a few seconds, and a 20amp breaker can hold it up to about 25 seconds.