Good catch, I made a subtraction error. The correct answer is 8.7W of resistive loss to support the 1.12 kVAr in my example, (edit: and 0.87% increased fuel consumption).
Cheers, Wayne
right, so the diff bewteen PF's means you needed to do more work on the gen side so you can deliver same P
watts of real power to the load. so in reality, the energy associated with X
L is wasted power. bad PF simply means more work to take a "kW package" from src to load.
its like UPS delivering to me daily a box. the box contains Y
work of energy everytime. UPS says "we will charge you $1 to deliver this box to you". everyone is happy until suddenly my office is 10 stories up and there is only stairs to get there. now all of a sudden UPS has to do more work to deliver the same box.
its takes work for UPS guy to climb the stairs against force of gravity, he reached 10th floor, now has a bunch of potential energy. that energy is also wasted energy because on his way down every step down is just a tad of heat, when he gets back to ground level all of the potential is gone, he is not standing there with the energy he put in to climb the stairs, its all wasted. he put in 1kJ to climb the stairs, he loses 1kJ on his way down.
climbing stairs and back down again is same as the reactance power Q. wasted, gone.