Orange grounding conductor....
Would you prefer a pink or purple GEC? Personally I think a bright yellow makes a bold statement.
Last edited:
Orange grounding conductor....
Would you prefer a pink or purple GEC? Personally I think a bright yellow makes a bold statement.
No, I spec pink and purple for switch legs.
I think the electrons will know exactly what to do when they see the color of the insulation.Orange grounding conductor and no grounding bushing?
Really? Separate ground. If a fault to ground occurs the path back to source is through the concrete rebar, to path of least resistance. Maybe to the ground rod. How soon would the breaker trip? May never trip. Let's see how long it takes to melt the breaker.I am not sure I see anything for sure wrong with what they did code wise.
I am not sure I see anything for sure wrong with what they did code wise.
There is an equipment ground pulled in with the feeders.
We had one client that asked for something like that. We told that that the only way we would do it, is if they gave us a letter directing us to make an installation that was both unsafe and a code violation. They would not do that, so we made the install per the code requirements for an "isolated ground".This particular brand is hardcore about having the IG on POS equipment. We always have to sign an affidavit at the end of the job to say it's correct and to their specs. We'll end up with about 50 receps total in 4000 sq ft of restaurant.
Most others have moved away from it, as it is really no longer needed with modern equipment. A couple of other restaurant brands we build also require it, but not to the level of the store pictured above.
Sent from my iPhone using Tapatalk
Is the separate ground bar attached to the other ground bar on left side of panel ? What bar is the egc from main panel connected to?There is an equipment ground pulled in with the feeders.
Is the separate ground bar attached to the other ground bar on left side of panel ? What bar is the egc from main panel connected to?
Sent from my SM-T350 using Tapatalk
Well, that makes a big difference. So, then we just have an auxiliary GEC and electrode for the panel. Probably useless, but legal.
Is the separate ground bar attached to the other ground bar on left side of panel ? What bar is the egc from main panel connected to?
Sent from my SM-T350 using Tapatalk
How many grounds do you need in that flex?It doesn't look like it.
This type of install is usually the result of an electrical contractor that's not purposely trying to do something wrong.
It generally that they simply don't know any better.
JAP>
How many grounds do you need in that flex?
Sent from my SM-T350 using Tapatalk
Yet the equipment (especially more modern equipment) apparently works even if there are ground loops.wow. failed to grasp the concept, eh?
the reason you want an isolated ground back to
the MAIN ground bus is to prevent ground loops,
that might bias solid state devices and cause madness.
but grounding all the devices to a point completely
different than the service ground virtually guarantees
a ground loop.
you can't fix stupid.
The feeder EGC lands on the EGC bus bolted directly to the cabinet. The left "neutral bus" which has all the "IG" conductors landed on it, has had it's jumper to the right neutral bus removed and is insulated from the EGC and the cabinet. All that connects to it is the "IG" conductors and the ground rod.There is an equipment ground pulled in with the feeders.