The feeder EGC lands on the EGC bus bolted directly to the cabinet. The left "neutral bus" which has all the "IG" conductors landed on it, has had it's jumper to the right neutral bus removed and is insulated from the EGC and the cabinet. All that connects to it is the "IG" conductors and the ground rod.
Used to be common to require all items that have communication links between them to be on the same line or phase as well as the isolated ground. May have been some justification to both at one time. Most newer equipment doesn't matter though.If we're going to pick it apart why are all of the 1p breakers on A phase only?
JAP>
Everything looks normal except that 5 of the branch circuits' egc's (including the mwbc) are only connected to their own ground rod.
I'm assuming the bar they're using to connect the isolated egc's and gec used to be a neutral bar with the factory jumper removed?
I wonder why only 1 of the 8 circuits are on L2?
Used to be common to require all items that have communication links between them to be on the same line or phase as well as the isolated ground. May have been some justification to both at one time. Most newer equipment doesn't matter though.
Because that is a red and it's a 2p breaker.
I was just joking earlier about only having black wire and that's why they landed all of the "Blacks" on A phase but that seems to be exactly what they did.
Had they extended the circuits with Red wire all of the breakers would have only been place on B Phase and A would have been left empty.
JAP>
What ever happened to balancing the load in that panel 1 phase has almost all load.Because that is a red and it's a 2p breaker.
I was just joking earlier about only having black wire and that's why they landed all of the "Blacks" on A phase but that seems to be exactly what they did.
Had they extended the circuits with Red wire all of the breakers would have only been place on B Phase and A would have been left empty.
JAP>
From what I understand it is mostly POS equipment and there probably is pretty minimal load to begin with. Might even been able to put them all on just one or two breakers and never had a trip on overload.What ever happened to balancing the load in that panel 1 phase has almost all load.
Sent from my SM-T350 using Tapatalk
If there isn't another voltage system on the premises, there is no requirement to identify each conductor by system and phase. The feeder conductors are both the same color. The feeder neutral needs to be white or gray and not taped if it is smaller then 4 AWG, which it looks like it may be.Even though the black and red are not oriented correctly on the 2p breaker if that's what they were trying to accomplish.
JAP>
If there isn't another voltage system on the premises, there is no requirement to identify each conductor by system and phase. The feeder conductors are both the same color. The feeder neutral needs to be white or gray and not taped if it is smaller then 4 AWG, which it looks like it may be.
It appears to me that the incoming wire EGC is connected to the ground bar on the right. the conduit EGC is connected to the box. So they are bonded together back at the source.
if it makes you feel better run a wire between the two ground bars.
It appears to me that the incoming wire EGC is connected to the ground bar on the right. the conduit EGC is connected to the box. So they are bonded together back at the source.
if it makes you feel better run a wire between the two ground bars.
That is good safety wise, but if it is required or requested to be isolated take all grounds separately back to the main.Just install the green screw laying in the bottom of the panel though the IG bar.