(11) Special care must be used to assure proper
grounding if NEC permitted isolated grounding is
specified. “Isolated/Insulated grounding” (IG) must
be per NEC Section 250-74; Connecting Receptacle
Terminal to Box; exception No. 4; and Section 250-
75, Bonding Other Enclosures for field wired (e.g.,
direct) branch circuit connections to electronic
equipment.
(12) In particular, no attempt must be made during or
after installation to separate the electronic system’s
equipment grounding conductors from the ac power
system’s equipment grounding conductors and its
associated earth electrode grounding connections.
Such separations would violate the NEC and
produce potential electrical fire and shock hazards.
They would also be likely to damage circuits inside
the related electronic equipment, or to at least
degrade the operation of it.
(13) Note that the use of the IG method even if it follows
NEC requirements, does not always improve the
performance of equipment. In fact, the use of the
IG wiring method is just as likely to make things
worse or to result in no observable change to the
operation of the equipment. There is usually no way
to predict the benefits if any, of isolated ground
circuits except by direct observation and
comparison between solid grounding (SG) and IG
methods in each case.
(14) It is relatively easy to convert existing IG circuits to
SG circuits on an as-needed basis. On the other
hand, it is generally both impractical and not cost
effective to convert an existing SG circuit to an IG
style that conforms to NEC requirements.
Accordingly, circuits used to supply power to
electronic equipment can be designed and first
installed as IG types, so that they may later be
converted back and forth between IG and SG as
needed.
(15) The equipment grounding conductors in a feeder or
branch circuit must always be routed within the
same conduit or raceway containing that circuit’s
associated power circuit conductors. This also
applies to flexible cord and cable assemblies.