I came across what IMO is a good example of resistive heating/installer error being relabeled as arcing or in this case "spark".
http://www.dailymail.co.uk/news/art...laze-caused-spark-dodgy-electrical-board.html
A professional analysis was done revealing otherwise:
https://www.surreycc.gov.uk/__data/...2/Fire-investigation-report-Clandon-Park-.pdf
It is theorized an over-tightened connection resulted in joule heating and a fire ensued from this condition:
What do you think, can an arc fault take the blame?
http://www.dailymail.co.uk/news/art...laze-caused-spark-dodgy-electrical-board.html
A professional analysis was done revealing otherwise:
https://www.surreycc.gov.uk/__data/...2/Fire-investigation-report-Clandon-Park-.pdf
It is theorized an over-tightened connection resulted in joule heating and a fire ensued from this condition:
In conclusion, the probable cause was a resistance heating fault on a neutral
bar in the electrical distribution board in the basement catching fire which was
not contained through adequate fire compartmentation, spreading quickly
throughout the entire building.
What do you think, can an arc fault take the blame?