So if the item needing clearance is 30 feet off the floor, which might leave it accessible but not necessarily readily accessible, then if they want a free working space you about need some kind of platform to stand on don't you?
You may need some means of access, but the code does not require it WRT working space requirements.
Or does NEC recognize that superman will be able to hover in front of this equipment, but still needs minimum of 30x36" of unobstructed space in front of such equipment?
Again, the code does not require ready access. You can go up with a ladder and work on it as far as the code is concerned.
I agree NEC doesn't specifically require a platform, but you need to have a way to get to the item regardless, and if you put a platform there then I would think it needs to allow for 110.26 clearances, a 12 x 18 inch surface might be something one can stand on but is not enough for 110.26.
How about a ladder rung in front of the area needing working space to stand on?
I agree if you put a platform there it has to comply with the working space requirements.
110.26 does cover height of work space as well. There is a lot of equipment in crawl spaces out there that doesn't comply with work space height requirements, question ultimately becomes what does need to comply? Likely to require service while energized - seems likely with a lot of HVAC equipment, yet a lot of what is installed never fully complies with 110.26.
I also agree a lot of equipment is installed that does not meet the working space requirements. That does not mean such an install meets code. It still does not meet code, even if it gets a passing grade from an inspector.