Hello,
We are in the process of finalizing the construction of a new maintenance building. There has been no problems with the design and the city has approved the permitting and the MEP design has been pretty thorough. Well to make a long story short. The electrical inspector came to perform his inspections and went through everything. There were no major issues found during the inspection, however when he got around to the closet HVAC unit which is a thru wall PTAC system he stated that the unit needed 3' clearance in front, because the unit has a integral switch that is inside of the unit. Now, I have never seen any inspector be so anal about something like this. Like I said the unit has an integral switch and the closet footprint was design per the manufacturers drawings. At this point the layout of the closet has been built by the contrator and the wall directly in front of the unit can not be modified, because it has stub up conduits through the concrete running up inside that wall. So, my question is, how can this matter be addressed and has anyone seen anything like this?
I have attached the manufacturers layout and the architect and mechanical team used this as a go by, but the inspector is making this into an maintenance and electrical issue. Now the layout that I have attached only shows the unit to have 12-inches in front however, the closet that has been built has approximately 18-19-inches in front of the unit. Also, to add the door on the side of the unit is 30-inches wide. The only way the unit can be service is if the unit is turned off, slid out and rotate 90-degrees and per the manufacturers the unit has to be removed off the wall in order to be serviced. In addition the 208V, 1phase service to the unit is being fed by panelboard that is within sight of the unit. The contractor also added an inline toggle switch as additional precautionary safety measures next to the unit inside the closet.
The only solution I can come up is to remove the inline toggle switch and install a 30A,2P non-fusible switch (blade type) on the outside of the closet and have that as the primary disconnecting and this will have more than enough clearance in front of the disconnect. However, there still is the integral disconnect switch inside of the unit and the inspector is saying that we would have to install terminal blocks inside of the unit and this derate the unit and we will have to get this unit relisted. At this point i'm lost for words with this inspector and we have offer a few options to rectify this and this guy won't let up. I think he couldn't return in the office empty handed, so he had to find something to justify he did his job.
Can anyone recommend a solution to this problem, so we can justify that the current configuration works as is or please share some insight if you have experienced such type installations.
Best Regards,
CoolJames :rant:

We are in the process of finalizing the construction of a new maintenance building. There has been no problems with the design and the city has approved the permitting and the MEP design has been pretty thorough. Well to make a long story short. The electrical inspector came to perform his inspections and went through everything. There were no major issues found during the inspection, however when he got around to the closet HVAC unit which is a thru wall PTAC system he stated that the unit needed 3' clearance in front, because the unit has a integral switch that is inside of the unit. Now, I have never seen any inspector be so anal about something like this. Like I said the unit has an integral switch and the closet footprint was design per the manufacturers drawings. At this point the layout of the closet has been built by the contrator and the wall directly in front of the unit can not be modified, because it has stub up conduits through the concrete running up inside that wall. So, my question is, how can this matter be addressed and has anyone seen anything like this?
I have attached the manufacturers layout and the architect and mechanical team used this as a go by, but the inspector is making this into an maintenance and electrical issue. Now the layout that I have attached only shows the unit to have 12-inches in front however, the closet that has been built has approximately 18-19-inches in front of the unit. Also, to add the door on the side of the unit is 30-inches wide. The only way the unit can be service is if the unit is turned off, slid out and rotate 90-degrees and per the manufacturers the unit has to be removed off the wall in order to be serviced. In addition the 208V, 1phase service to the unit is being fed by panelboard that is within sight of the unit. The contractor also added an inline toggle switch as additional precautionary safety measures next to the unit inside the closet.
The only solution I can come up is to remove the inline toggle switch and install a 30A,2P non-fusible switch (blade type) on the outside of the closet and have that as the primary disconnecting and this will have more than enough clearance in front of the disconnect. However, there still is the integral disconnect switch inside of the unit and the inspector is saying that we would have to install terminal blocks inside of the unit and this derate the unit and we will have to get this unit relisted. At this point i'm lost for words with this inspector and we have offer a few options to rectify this and this guy won't let up. I think he couldn't return in the office empty handed, so he had to find something to justify he did his job.
Can anyone recommend a solution to this problem, so we can justify that the current configuration works as is or please share some insight if you have experienced such type installations.