We have installed a 45kva transformer 480vac 150amp incoming and 208/120vac 100amp outgoing. The transformer is mounted on a building steel column as well as the secondary 100amp fused disconnect it is servicing.
The question I have is on the Neutral bonding.
The neutral/ground bond was done in the disconnect with the bond screw 250.30 first disconnecting means. The grounding electrode is connected to the transformer case then run to the disconnects ground terminal is this acceptable?
Thank you for any response
The question I have is on the Neutral bonding.
The neutral/ground bond was done in the disconnect with the bond screw 250.30 first disconnecting means. The grounding electrode is connected to the transformer case then run to the disconnects ground terminal is this acceptable?
Thank you for any response