From the discussions on other threads, I have concluded that transformer loading should always be computed to be the sum of Vphase x Iphase rather than summing up the individual loads. Why you ask?
It turns out that connecting unbalanced line to line loads on a 3-phase wye yields different loadings depending on the way you compute them. Take the infamous Oregon state test question involving the magic number, 1.154. The load thinks it is getting 208xI VA, but the transformer thinks it is delivering 2x120xI VA. How would you size the tranformer? Use the larger number of course.
I would expect however, that the loads would be more nearly balanced, and this would be less of a problem. Still, it makes sense to compute the loading from VphasexIphase.
This is the dead horse Ed brought up recently, but it is an important dead horse. One would not knowingly undersize a tranformer by 15%.
I expect to hear a bit of rebuttal on this.
It turns out that connecting unbalanced line to line loads on a 3-phase wye yields different loadings depending on the way you compute them. Take the infamous Oregon state test question involving the magic number, 1.154. The load thinks it is getting 208xI VA, but the transformer thinks it is delivering 2x120xI VA. How would you size the tranformer? Use the larger number of course.