Originally posted by jim dungar:
rattus
Please show me your calculations. My formulas simply determine each individual winding VA which are then added vectorially due to the time domain difference between Van and Vnc.
Jim, my calculations are simple:
Papp = Vphase x Iphase (per xfrmr)
Preal = Papp x cos(30) (xfrmr to load)
Let me restate my position:
Different load configurations do not affect xfrmr loading. For the same current and voltage, the same heat is generated in the core and windings however the load is arranged. It is illogical to say the loading is 2080VA in one case and 2400VA in the other.
I will now repeat for the umpteenth time that power is not a vector quantity, therefore it is nonsense to add powers vectorially. I doubt that you do that when figuring loads in the conventional manner. That seems to be the sticking point.
There really is a per phase apparent power, and there really is a basis for the Oregon factor.
Where I lived in Africa, the homes were wired 380/220. The water heaters were wired on one phase and "controlled" by a local contactor. As an energy conservation method the "water-heater" phase was opened periodically by the local utility. The process was rotated throughout the city.Originally posted by rattus:
I have a question: Is there ever a case where only two phases from a wye xfrmr are used? I can't believe anyone would do that on purpose.
I don't think I had any comment on this. I checkedIf you and Jim would just concede that power is a scalar quantity and cannot be added vectorially, this discussion would be at an end
Then total VA is Pan + Pcn + Q an + Qcn orPan = 120*10*.866 = 1040W
Qan = 120*10*.5 = 600VAR
VAan = 1200VA
Pcn = 120*10*.866 = 1040W
Qcn = 120*10*-.5 = -600VAR
VAcn = 1200VA
I hope by now that even Bob the consultant will admit there is a PF in the secondaries. But the real issue is, "What is the loading on the transformers?"Originally posted by jim dungar:
rattus,
I never said power (P) was a vector. I said VA was a vector made up of scalar components P and Q.
Reply: Jim, apparent power is still not a vector. To be a vector the waveform would have to be sinusoidal which it is not. Furthermore, you cannot vector away any heat generated in the transformer.
And after reviewing your calculations, you are correct it is "tricky", I never new that the inverse of Ic=10A @ -150?, was -Ic=10A @ -30?.
I always believed that it was,
10 @ -150? - 180? = 10 @ 30?,
Reply: Typo Jim, typo! My good eye has stitches in it!
which would make the current into Vcn equal to the current leaving Van satisfying almost every network analysis I know of.
Originally posted by jim dungar:
But I still can not accept your conclusion.
In both of your situations the current through each winding is equal and in the same direction, or else there would be a residual current In. If the vector current in each winding is the same then the VA loading of the transformer must be the same.
Reply: But Jim, that is my conclusion and has been since day 1! Also, as long as the currents are equal in magnitude, and even if In is not zero, the same argument prevails. Are you switching sides on me?
Also, this is not a uniquely special case. Wye connected transformers are routinely severely unbalanced.
Reply: If that is the case, then loading should be computed as Vphase x Iphase.
Jim, please support that argument with some sort of physical principle or law.Originally posted by jim dungar:
No, I am not switching sides. The transformer winding loading is always 1200VA each and the total transformer loading is 2080VA. If there is no neutral current then the two series connected loads must be identical in loading to a single load.