4.1.6.1 Capability
Transformers shall be capable of
a) Operating continuously above rated voltage or below rated frequency, at maximum rated kVA for any tap, without exceeding the limits of observable temperature rise in accordance with 5.1 1.1 when all of the following conditions prevail:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">1) Secondary voltage and volts per hertz do not exceed 105% of rated values.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">2) Load power factor is 80% or higher.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">3) Frequency is at least 95% of rated value.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">b) Operating continuously above rated voltage or below rated frequency, on any tap at no load, without exceeding limits of observable temperature rise in accordance with 5.1 1.1, when neither the voltage nor volts per hertz exceed 110% of rated values.