Transformer Loading:

Status
Not open for further replies.
Re: Transformer Loading:

Originally posted by rattus:What many seem to be missing though is that the individual transformers see 120V x I VA as their apparent load. You do not apply vectors to apparent power. You add apparent power arithmetically. The transformers deliver 2400VA.
Rattus, your logic is completely flawed. The value 2400 has no place in this discussion. There is a fundamental truth that you are missing: conservation of energy. Here is the truth:
The transformer supplies the exact same amount of apparent power as is absorbed by the load.
{ASIDE: This statement disregards losses, but the losses are small. Loses would not account for the difference between 2080 and 2400 anyway, so it is OK to disregard them. }

You are mixing the concepts of instantaneous power and average power. Specifically, when you try to add IaVa to IbVb, and get (10)(120) + (10)(120) = 2400, you are using instantaneous values and calling it an average power. That does not work ? you can?t mix the two, as you have said before, and as you have quoted a professor has having confirmed.

Power is constant in a balanced three-phase system. That is why we can use the following general process for calculating a value for service or feeder current.
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Take the current drawn by each single phase 120 volt load, and multiply by 120.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Take the current drawn by each single phase 208 volt load, and multiply by 208.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Take the current drawn by each three phase 208 volt load, and multiply by 208 x 1.732.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Add up all these values.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Divide by 208 x 1.732 to get the total current.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
Inherent in this process is the presumption of an at least ?roughly balanced? system. If it is not balanced, then this process fails us. This process only works because the VA produced in each transformer winding ? none one of the three being constant, but rather each varies instant by instant ? when added to the VA produced in the other two windings, gives a formula for the total VA in which the variable ?time? is eliminated. Power is constant only in the sum of the three balanced phases. Power is not constant in any single phase 120 volt load, nor in any single phase 208 volt load.

You are taking the 10 amps of each of two transformer secondary windings, multiplying it by the 120 volts across each winding, and getting a total of 2400 VA. That is invalid, specifically because the total apparent power in this configuration is not constant. At the instant when one of the two windings is producing a maximum VA, the other winding is producing less than the maximum VA. The total of the two is not a simple arithmetic sum of 1200 plus 1200. We usually add the VA of all loads arithmetically, but again that only works because we are dealing with balanced three-phase systems. For the three-phase transformer that feeds only a single load, and that load being a single phase 208 volt load, the overall system is not balanced, so the total VA will vary moment to moment.

If you wish to calculate the total VA produced by a transformer with a single-phase 208 volt load, you must either use phasor (vector) addition or use fundamental trigonometry. When you do either, you will get an answer of 2080 VA, not 2400 VA.
 
Re: Transformer Loading:

Rattus I understand all that but all the 1.154 does is make the 208 appear to be 240 right?

What does the 208 verses 240 have to do with apparent or real power it is what it is coming off the lugs of the transformer 208 or 240 in this case it would be Wye 208 or 240 delta.Then if the branch circuit had a inductor or capacitance in it would have a power factor which you would use your arithmetic to figure real power.

I didn't understand what you said above because line to neutral would be 120 and line to line would be 208? 1.73 x the power with 208.

Ronald :)

[ March 09, 2005, 12:52 PM: Message edited by: ronaldrc ]
 
Re: Transformer Loading:

Originally posted by jim dungar:
rattus,

Your/their reasoning is not tricky, it is wrong.
And yes, after applying transformers for 26 years, I do understand 3 phase perfectly fine.

Power factor is the phase angle difference between voltage (E) and current (I). It has nothing to do with the phase angle differences between voltages.

Also remember the relationship of phase to phase voltage (Epp) and phase to neutral voltages (Epn). These relationships are fixed and cannot be modified simply by dropping a phase or neutral connection.
Single phase: Epp = 2*Epn
three phase: Epp = 1.73*Epn
 
Re: Transformer Loading:

rattus
I think there have been 23 responses to you question. If you take out your response the remaining 16 say that your are wrong. What does it take for you to get that. Is everyone else
wrong and you are the only one right?

Your post
Now consider separate lads across the two phase voltages:
A 12 Ohm @ -30 load from Va to neutral, and
A 12 Ohm @ 30 load from Vc to neutral.
Resistance load does not have an angle associated with it. If you had XL or XC, then an angle would
be correct.
To associate an angle with the R is incorrect.

Now work out the currents and the power.
You will find that the currents are exactly the same in both cases, but the xfrmr does not know the difference, nor does it care. It only knows it is being saddled with 1200VA per winding, not 1040VA.
You may have this partly correct. If the load amps is 10 amps the VA per phase is 120 x 10 = 1200 VA.
That is the per phase power. If you check out the
sine wave drawing that ron posted you will see that Phase A voltage is at peak when Phase B is at a negative value of about -.5 x 120. The load on the transformer is occuring at different time intervals. This is what the guys have been saying.
You can not add 1200 VA and 1200 VA and get 2400 VA.
ronald, I understand all that perfectly. What many seem to be missing though is that the individual transformers see 120V x I VA as their apparent load. You do not apply vectors to apparent power. You add apparent power arithmetically. The transformers deliver 2400VA.
Well obviously this is incorrect also. Since the load is resistive the Apparent Power (VA) and the Real Power (Watts) is the same value since the power factor is 1.

Then if someone replaces that load in the black box with a line to line load which also draws 10A, you would say the transformer delivers 120 V x 10A because the transformer does not know the difference
I would not say that. It should be 208 volts x 10.
There is a difference between the Line Voltage and the phase voltage.

It is tricky, but once you get your mind wrapped around it, you will understand 3-phase better
I can not believe you said that.
Charlie B said
Rattus, your logic is completely flawed. The value 2400 has no place in this discussion. There is a fundamental truth that you are missing: conservation of energy.
Thats right on the mark

[ March 09, 2005, 04:36 PM: Message edited by: bob ]
 
Re: Transformer Loading:

Bob,

This is not a popularity contest. It is a search for truth.

You are missing some basic points regarding phase angles and putting words in my mouth that I did not utter. I have presented a detailed scenario which you obviously did not follow. All phase angles should be referenced to the positive x-axis, not to each other.

Now I believe that at least one moderator has agreed with me. His vote should count for something.

The difference of opinion occurs I believe arises because the power industry relies on standard formulas which are quite valid, but in this case one must approach the problem from the basics.

I have invited you to have a private debate on this matter, but you have so far declined. Instead you make blanket statements questioning my credibility. Are you ready for the challenge?

[ March 09, 2005, 02:58 PM: Message edited by: rattus ]
 
Re: Transformer Loading:

rattus
You are missing some basic points regarding phase angles and putting words in my mouth that I did not utter.
I just took what you posted and made my comments.

I have presented a detailed scenario which you obviously did not follow. All phase angles should be referenced to the positive x-axis, not to each other.
I'm not sure where this fits.

The difference of opinion occurs I believe arises because the power industry relies on standard formulas which are quite valid, but in this case one must approach the problem from the basics.
Which formulas are not correct?
 
Re: Transformer Loading:

Originally posted by jim dungar:
rattus,

Your/their reasoning is not tricky, it is wrong.
And yes, after applying transformers for 26 years, I do understand 3 phase perfectly fine.

Reply: Yes Jim, but some do not.

Reply: Power factor is the phase angle difference between voltage (E) and current (I). It has nothing to do with the phase angle differences between voltages.

Yes Jim, I know that too, and I insist that there is a PF of 87% in the transformer secondaries. That is the reason that 2400VA from the transformers delivers 2080W to the load. Real power is constant in the system, not apparent power, and it has nothing to do with instantaneous values.

Also remember the relationship of phase to phase voltage (Epp) and phase to neutral voltages (Epn). These relationships are fixed and cannot be modified simply by dropping a phase or neutral connection.
Single phase: Epp = 2*Epn
three phase: Epp = 1.73*Epn

Reply: Yes Jim, I know that too. I never said otherwise. I have even zinged Ed for claiming 60 degree separation in a delta config.

Let me try one more time to get my point across. Imagine that these two transformers are rated at 1040VA each. Now convert this to a current rating, which is what it boils down to,

Imax = 1040VA/120A = 8.7A,

Now apply the line to line load of 10A @ 208V. You have exceeded the rating of the transformer. Explain this anomaly. If you can't, then you cannot say I am wrong.

Also, it seemed for a while that some understood the basis for the infamous Oregon factor, but it seems now that most have regressed to their first notions and insist on talking balanced loads which this is not.

Maybe someone could consider my post detailing the various phase angles and tell me specifically where I am wrong. So far no one has even attempted that.

Rattus,
BSEE, MSEE, and 40 plus years since.

[ March 09, 2005, 03:31 PM: Message edited by: rattus ]
 
Re: Transformer Loading:

Thanks Bob

Good to know someone checked my drawing out it took me a good while to draw that one.

I have been in the trade for over 30 years and I never really understood 3 phase but now I believe I have a handle on it.I knew enough to trouble shoot and hook up machines but not the mechanics of how it was produced.

Whats so funny is most of this knowledge came from what Rattus had told to me in private post.

If you will examine the graph not only is B phase neg. But B phase and C phase are both neg. at 50 volts and this is added together and at that point the positive peak of A phase is canceled out to Zero.

Edited because I'm not sure thats right weres Ed?

Ronald :)

[ March 09, 2005, 03:43 PM: Message edited by: ronaldrc ]
 
Re: Transformer Loading:

Originally posted by bob:
rattus

Your post
Now consider separate lads across the two phase voltages:
A 12 Ohm @ -30 load from Va to neutral, and
A 12 Ohm @ 30 load from Vc to neutral.
Resistance load does not have an angle associated with it. If you had XL or XC, then an angle would
be correct.
To associate an angle with the R is incorrect.

Reply: Bob, you should recognize that these are impedances. A pure resistance would carry an angle of zero.
Now work out the currents and the power.
You will find that the currents are exactly the same in both cases, but the xfrmr does not know the difference, nor does it care. It only knows it is being saddled with 1200VA per winding, not 1040VA.
You may have this partly correct. If the load amps is 10 amps the VA per phase is 120 x 10 = 1200 VA.
That is the per phase power. If you check out the
sine wave drawing that ron posted you will see that Phase A voltage is at peak when Phase B is at a negative value of about -.5 x 120. The load on the transformer is occluding at different time intervals. This is what the guys have been saying.
You can not add 1200 VA and 1200 VA and get 2400 VA.

Reply: Power, real or apparent, is not a vector quantity and must be added arithmetically.

ronald, I understand all that perfectly. What many seem to be missing though is that the individual transformers see 120V x I VA as their apparent load. You do not apply vectors to apparent power. You add apparent power arithmetically. The transformers deliver 2400VA.
Well obviously this is incorrect also. Since the load is resistive the Apparent Power (VA) and the Real Power (Watts) is the same value since the power factor is 1.

Reply: There is a single current. The PF cannot be 1 in the load and in the transformer secondaries where the phase voltage angles are different from the phase angle of the load voltage. Until you grasp that fact, you will never understand this analysis. This point should be crystal clear to anyone who claims to understand phase angles and power factor.

Then if someone replaces that load in the black box with a line to line load which also draws 10A, you would say the transformer delivers 120 V x 10A because the transformer does not know the difference
I would not say that. It should be 208 volts x 10.
There is a difference between the Line Voltage and the phase voltage.

Reply: The point is that you DO NOT KNOW what is in the black box. You do not know how the load is connected. You only know that the currents are exactly the same. So how do you compute the load?

It is tricky, but once you get your mind wrapped around it, you will understand 3-phase better
I can not believe you said that.

Reply: I stand by that statement.

Charlie B said
Rattus, your logic is completely flawed. The value 2400 has no place in this discussion. There is a fundamental truth that you are missing: conservation of energy.

Reply: Charlie B. said "energy". Apparent power is not energy. Real power is constant in the system, not apparent power, certainly not in this case of a severely unbalanced system. 2400 x cos(30) = 2400 x 0.87 = 2080. Charlie B. is wrong although he is slow to admit it.
 
Re: Transformer Loading:

Dag gone Rattus we can't tell whats what when you holler like that. I not saying that you are wrong but I haven't seen anyone on here perfect yet.I will be the first to admit its the sharpest crowd I personally have ever discussed this field with of course being from Tennessee that might not be saying much.

When I screw up I admit it theres a few on here that don't.I hope you don't join that crowd.There I've made another enemy, but just being honest.
 
Re: Transformer Loading:

Since I appear to be the ?culprit? moderator, I guess I?ll add another comment.

A great deal of the difference is a matter of approach, the engineer?s vs. the physicist?s. On a day-to-day basis, I?m usually interested in the ?practical.? If I had to do all my work deriving the calcs from Maxwell?s equations I still wouldn?t be finished with my first project, begun in the late 60?s. Nevertheless, occasionally it is not only valuable, but also necessary, to review the true ?physics? of an issue.

I said in another post, for an ideal transformer, the throughput in the circuit under discussion would be 2080Ws and 1200VARs, assuming a purely resistive load. That is what properly installed metering would indicate ? whether on the primary or secondary of the transformer and whether the primary was wye or delta connected.

Most of us would say that is 2400VA. I deliberately avoided it. Watts and VARs have true, physical meaning: the rate energy is used and rate that energy is stored and returned to the system from the magnetic fields. In this case, the 1200VARs would be cycled between the magnetic fields of the two involved windings. They would never ?see the light of day? outside the transformer.

VA does not have real physical meaning ? but it IS practical. With only a couple of provisos, relatively high load power-factors and loads ?relatively balanced? on all three phases, everything works fine because we don?t use ?ideal? transformers and the ones we do use have the tolerance to accommodate minor differences.

Occasionally, the loads are seriously imbalanced or they have terrible power factors or both. In those cases, we have to review the effect on the transformer, and I believe that is some of what rattus is getting at; the need of that review is something that I believe most of us are already in agreement.

I believe the open question is whether the transformer loading is effectively Vphase x Iphase in VA regardless of the load configuration. Assuming that Vphase is the measured voltage across the winding and Iphase the measured current through it, my opinion is a very qualified ?yes? for a given single winding. Does this mean the transformer under discussion ?sees? 2400VA? I don?t know, I can only say that since power transformers are current limited regardless of the output voltage it is the equivalent effect of 1200VA on each of two windings.
 
Re: Transformer Loading:

Rattus,

What you have said makes perfect sense to me.

Didn't the NEC get away from "watts" and go to "VA" in order to make sure the conductors (and I would guess transformers) can handle the apparent power?
 
Re: Transformer Loading:

rattus,

Are you taking the long way to say that an open wye transformer bank cannot support the same three phase loading as a "closed" wye?

Going back to your March 4 17:18 post.
The wye transformer bank sees a 20.8 ohm phase to phase load identical to 2 separate 12 ohm phase to neutral loads. The effective load is 2080VA.

p = phase
n = neutral
w = winding
pp = phase to phase
pn = phase to neutral
a = phase a
c = phase c
t = total

Case 1, 20.8 ohm load phase to phase
Vpp = 208V
Vw = Vpn = Vpp/1.73 = 208V/1.73 = 120V
Ip = Vpp/Zpp = 208/20.8 = 10A
Iw = Ip = 10A
VAw = Vw*Iw = 120*10 = 1200VA
VAt = Vpp*Ip = (Vw*1.73)*Iw = 2080VA

Case 2, 12 ohm load phase to neutral
Vpn = 120V
Vw = Vpn = 120V
Ip = Vpn/Zpn = 120/12 = 10A
Iw = Ip = 10A
VAw = Vw*Iw = 120*10 = 1200VA
VAt = Vwa*Iw + Vwc*Iw = (Vwa+Vwc)*Iw = Vpp*Iw = 208*10 = 2080VA

Assuming these are full load values, a closed wye transformer would be: VAt = 3*VAw = 3*1200 = 3600VA. But because this is an open wye arrangement the effective three phase rating is only 57.77% of 3600VA, or 2080VA. But in neither case is any winding overloaded.

Now please explain how load power factor comes into any of the transformer VA calculations. Or, how total VA is a fictitious number.
 
Re: Transformer Loading:

Jim, let me quote from a post by grlsound:

"After consulting with not less than THREE electrical engineers, I think I may have a glimmer of an idea as to where, and why, one might use that elusive factor. This example is of a purely resistive single phase load, DELTA connected to a WYE source. (ie: transformer) I am told that when this connection happens, the current and voltage become out of phase by 30 degrees. (phasor diagrams in many engineering books). This appears to be related to something similar to power factor. The resistive load will not add to the phase shift, will not subtract from that out of phase voltage and current, but WILL NOT be able to generate its rated wattage due to the current phase shift away from the voltage. Please do not ask me WHY that phase shift occurs. I do not know. I do know that both of my electrical engineering books say that it does occur. That elusive factor is the reciprocal of the cosine of 30 degrees."

grlsound reports that three, count them, EEs agree that the wye phase currents and wye phase voltages are out of phase by 30 degrees. This is should be obvious from the vector diagram.

If we have a 30 degree shift between Vphase and Iphase, then the PF = cos(30) = 0.87. Then,
Preal = 2 x 10 x 120 x 0.87 = 2080W delivered by the transformer. PF in the load is 1.0.

In your critique of my example, you left the angles off my 12 Ohm loads. That is what makes the currents equivalent. No, they are not resistors, they are impedances.

I ask again, why should the load be different on two transformers driving the same current through 2 impedances to neutral as opposed to driving this current through a single impedance line to line? Give me a solid reason for that, and I will concede that I am dead wrong and don't even know the difference between resistance and impedance.

Now, for the real world, you will never see such an imbalanced load, so the standard methods work just fine.

Rattus,

BSEE, MSEE
 
Re: Transformer Loading:

My formulas work just as well with Z as with R. And yes I can imagine several possible real world load profiles that could unbalance a wye transformer as in your example.

What does the phase angle between the current and the voltage have to do with calculating the VA loading of a transformer? The only affect I can visualize is the resultant neutral current. But the specific value of the neutral current does not come into play when analyzing the loading of each individual winding.

And I can believe that there are at least three EEs that do not understand power relationships. Even as an EE myself, I would be out of my area of expertise in a discussion on electronics.
 
Re: Transformer Loading:

rasttus posted
Jim, let me quote from a post by grlsound:

"After consulting with not less than THREE electrical engineers, I think I may have a glimmer of an idea as to where, and why, one might use that elusive factor. This example is of a purely resistive single phase load, DELTA connected to a WYE source. (ie: transformer) I am told that when this connection happens, the current and voltage become out of phase by 30 degrees.

grlsound reports that three, count them, EEs agree that the wye phase currents and wye phase voltages are out of phase by 30 degrees. This is should be obvious from the vector diagram.
You have misquoted grlsound.
. He reports that the engineers said with a delta connected load the current and voltage is out of phase by 30 degrees. You then say that the wye phase current and wye phase voltage are out of phase by 30 degrees.
Neither of you are correct. In a balanced delta connected load the line current is sqrt of 3 x phase current and it is out of phase with the component phase current by
30 degrees. You can't have it both ways.
Sence the phase shift is out I assume the following is out also.
If we have a 30 degree shift between Vphase and Iphase, then the PF = cos(30) = 0.87. Then,
Preal = 2 x 10 x 120 x 0.87 = 2080W delivered by the transformer. PF in the load is 1.0.
Edit to remove the term balanced from the post.

[ March 10, 2005, 08:58 AM: Message edited by: bob ]
 
Re: Transformer Loading:

Originally posted by bob:
rasttus posted
Jim, let me quote from a post by grlsound:

"After consulting with not less than THREE electrical engineers, I think I may have a glimmer of an idea as to where, and why, one might use that elusive factor. This example is of a purely resistive single phase load, DELTA connected to a WYE source. (ie: transformer) I am told that when this connection happens, the current and voltage become out of phase by 30 degrees.

grlsound reports that three, count them, EEs agree that the wye phase currents and wye phase voltages are out of phase by 30 degrees. This is should be obvious from the vector diagram.
You have misquoted grlsound.

He reports that the engineers said with a balanced delta connected load the current and voltage is out of phase by 30 degrees. You then say that the wye phase current and wye phase voltage are out of phase by 30 degrees.
Neither of you are correct. In a balanced delta connected load the line current is sqrt of 3 x phase current and it is out of phase with the component phase current by
30 degrees. You can't have it both ways.
No, I did not misquote, this is a cut and paste. And, he did not say it was a balanced delta either. It was a "single phase load, DELTA connected". The word "balanced" does not appear in the quote. If you continue to misread the text, you will never understand this. You appear to be sniping, trying to find some fault where none exists.

You have suggested that I consult with someone more knowledgeable than I, and I know a number of them. I have consulted with two of them, both geniuses, and they say I am right.

Rattus
 
Re: Transformer Loading:

Originally posted by jim dungar:
My formulas work just as well with Z as with R. And yes I can imagine several possible real world load profiles that could unbalance a wye transformer as in your example.

Reply: Jim, of course they do. The point of the 12 Ohms @ 30 degrees to neutral is that this load provides the exact same current and phase as 20.8 Ohms @ 0 line to line. In one case the apparent power you calculate to be 2080VA, In the other it is 2400VA.

The same current through the same winding provides different apparent powers? How can this be? No one has answered this yet!

What does the phase angle between the current and the voltage have to do with calculating the VA loading of a transformer? The only affect I can visualize is the resultant neutral current. But the specific value of the neutral current does not come into play when analyzing the loading of each individual winding.

Reply: Nothing to do with apparent power, but it correlates real to apparent power.

2400VA x 0.87 = 2080W

And I can believe that there are at least three EEs that do not understand power relationships. Even as an EE myself, I would be out of my area of expertise in a discussion on electronics.

Reply: Jim this remark is unprofessional. Why don't you try to understand what is being said instead of criticizing people you do not know.

If you would work out the vector diagrams for this problem, I think you would see the light. Forget the standard formulas for the moment. Attack the problem from the basics.

Power is something taught in the old days, and a few of us have made the effort to retain this knowledge. I believe the EEs of today receive little or no schooling in AC circuits and power.

Now if someone has access to a circuit simulator, they could simulate this problem in seconds and see the various voltages, currents, and angles. I can't make my PSPICE work right, or I would do it myself.


[ March 10, 2005, 01:02 AM: Message edited by: rattus ]
 
Re: Transformer Loading:

Originally posted by hardworkingstiff:
Rattus,

What you have said makes perfect sense to me.

Didn't the NEC get away from "watts" and go to "VA" in order to make sure the conductors (and I would guess transformers) can handle the apparent power?
Stiff, my thought is that apparent power is a convenient way to tally up loading without having to bother with power factor and separating the single phase and three phase loads. Don't know what the NEC says about it, but it was taught in the EE schools 50 years ago.
 