- Location
- Mission Viejo, CA
- Occupation
- Professional Electrical Engineer
Re: Transformer Loading:
I guess I should add that I'm ignoring "cooling" methods.
I guess I should add that I'm ignoring "cooling" methods.
Rattus, your logic is completely flawed. The value 2400 has no place in this discussion. There is a fundamental truth that you are missing: conservation of energy. Here is the truth:Originally posted by rattus:What many seem to be missing though is that the individual transformers see 120V x I VA as their apparent load. You do not apply vectors to apparent power. You add apparent power arithmetically. The transformers deliver 2400VA.
{ASIDE: This statement disregards losses, but the losses are small. Loses would not account for the difference between 2080 and 2400 anyway, so it is OK to disregard them. }The transformer supplies the exact same amount of apparent power as is absorbed by the load.
Originally posted by jim dungar:
rattus,
Your/their reasoning is not tricky, it is wrong.
And yes, after applying transformers for 26 years, I do understand 3 phase perfectly fine.
Power factor is the phase angle difference between voltage (E) and current (I). It has nothing to do with the phase angle differences between voltages.
Also remember the relationship of phase to phase voltage (Epp) and phase to neutral voltages (Epn). These relationships are fixed and cannot be modified simply by dropping a phase or neutral connection.
Single phase: Epp = 2*Epn
three phase: Epp = 1.73*Epn
Resistance load does not have an angle associated with it. If you had XL or XC, then an angle wouldNow consider separate lads across the two phase voltages:
A 12 Ohm @ -30 load from Va to neutral, and
A 12 Ohm @ 30 load from Vc to neutral.
You may have this partly correct. If the load amps is 10 amps the VA per phase is 120 x 10 = 1200 VA.Now work out the currents and the power.
You will find that the currents are exactly the same in both cases, but the xfrmr does not know the difference, nor does it care. It only knows it is being saddled with 1200VA per winding, not 1040VA.
Well obviously this is incorrect also. Since the load is resistive the Apparent Power (VA) and the Real Power (Watts) is the same value since the power factor is 1.ronald, I understand all that perfectly. What many seem to be missing though is that the individual transformers see 120V x I VA as their apparent load. You do not apply vectors to apparent power. You add apparent power arithmetically. The transformers deliver 2400VA.
I would not say that. It should be 208 volts x 10.Then if someone replaces that load in the black box with a line to line load which also draws 10A, you would say the transformer delivers 120 V x 10A because the transformer does not know the difference
I can not believe you said that.It is tricky, but once you get your mind wrapped around it, you will understand 3-phase better
Thats right on the markRattus, your logic is completely flawed. The value 2400 has no place in this discussion. There is a fundamental truth that you are missing: conservation of energy.
I just took what you posted and made my comments.You are missing some basic points regarding phase angles and putting words in my mouth that I did not utter.
I'm not sure where this fits.I have presented a detailed scenario which you obviously did not follow. All phase angles should be referenced to the positive x-axis, not to each other.
Which formulas are not correct?The difference of opinion occurs I believe arises because the power industry relies on standard formulas which are quite valid, but in this case one must approach the problem from the basics.
Originally posted by jim dungar:
rattus,
Your/their reasoning is not tricky, it is wrong.
And yes, after applying transformers for 26 years, I do understand 3 phase perfectly fine.
Reply: Yes Jim, but some do not.
Reply: Power factor is the phase angle difference between voltage (E) and current (I). It has nothing to do with the phase angle differences between voltages.
Yes Jim, I know that too, and I insist that there is a PF of 87% in the transformer secondaries. That is the reason that 2400VA from the transformers delivers 2080W to the load. Real power is constant in the system, not apparent power, and it has nothing to do with instantaneous values.
Also remember the relationship of phase to phase voltage (Epp) and phase to neutral voltages (Epn). These relationships are fixed and cannot be modified simply by dropping a phase or neutral connection.
Single phase: Epp = 2*Epn
three phase: Epp = 1.73*Epn
Reply: Yes Jim, I know that too. I never said otherwise. I have even zinged Ed for claiming 60 degree separation in a delta config.
Let me try one more time to get my point across. Imagine that these two transformers are rated at 1040VA each. Now convert this to a current rating, which is what it boils down to,
Imax = 1040VA/120A = 8.7A,
Now apply the line to line load of 10A @ 208V. You have exceeded the rating of the transformer. Explain this anomaly. If you can't, then you cannot say I am wrong.
Also, it seemed for a while that some understood the basis for the infamous Oregon factor, but it seems now that most have regressed to their first notions and insist on talking balanced loads which this is not.
Maybe someone could consider my post detailing the various phase angles and tell me specifically where I am wrong. So far no one has even attempted that.
Rattus,
BSEE, MSEE, and 40 plus years since.
Originally posted by bob:
rattus
Your postResistance load does not have an angle associated with it. If you had XL or XC, then an angle wouldNow consider separate lads across the two phase voltages:
A 12 Ohm @ -30 load from Va to neutral, and
A 12 Ohm @ 30 load from Vc to neutral.
be correct.
To associate an angle with the R is incorrect.
Reply: Bob, you should recognize that these are impedances. A pure resistance would carry an angle of zero.
You may have this partly correct. If the load amps is 10 amps the VA per phase is 120 x 10 = 1200 VA.Now work out the currents and the power.
You will find that the currents are exactly the same in both cases, but the xfrmr does not know the difference, nor does it care. It only knows it is being saddled with 1200VA per winding, not 1040VA.
That is the per phase power. If you check out the
sine wave drawing that ron posted you will see that Phase A voltage is at peak when Phase B is at a negative value of about -.5 x 120. The load on the transformer is occluding at different time intervals. This is what the guys have been saying.
You can not add 1200 VA and 1200 VA and get 2400 VA.
Reply: Power, real or apparent, is not a vector quantity and must be added arithmetically.
Well obviously this is incorrect also. Since the load is resistive the Apparent Power (VA) and the Real Power (Watts) is the same value since the power factor is 1.ronald, I understand all that perfectly. What many seem to be missing though is that the individual transformers see 120V x I VA as their apparent load. You do not apply vectors to apparent power. You add apparent power arithmetically. The transformers deliver 2400VA.
Reply: There is a single current. The PF cannot be 1 in the load and in the transformer secondaries where the phase voltage angles are different from the phase angle of the load voltage. Until you grasp that fact, you will never understand this analysis. This point should be crystal clear to anyone who claims to understand phase angles and power factor.
I would not say that. It should be 208 volts x 10.Then if someone replaces that load in the black box with a line to line load which also draws 10A, you would say the transformer delivers 120 V x 10A because the transformer does not know the difference
There is a difference between the Line Voltage and the phase voltage.
Reply: The point is that you DO NOT KNOW what is in the black box. You do not know how the load is connected. You only know that the currents are exactly the same. So how do you compute the load?
I can not believe you said that.It is tricky, but once you get your mind wrapped around it, you will understand 3-phase better
Reply: I stand by that statement.
Charlie B said
Rattus, your logic is completely flawed. The value 2400 has no place in this discussion. There is a fundamental truth that you are missing: conservation of energy.
Reply: Charlie B. said "energy". Apparent power is not energy. Real power is constant in the system, not apparent power, certainly not in this case of a severely unbalanced system. 2400 x cos(30) = 2400 x 0.87 = 2080. Charlie B. is wrong although he is slow to admit it.
You have misquoted grlsound.Jim, let me quote from a post by grlsound:
"After consulting with not less than THREE electrical engineers, I think I may have a glimmer of an idea as to where, and why, one might use that elusive factor. This example is of a purely resistive single phase load, DELTA connected to a WYE source. (ie: transformer) I am told that when this connection happens, the current and voltage become out of phase by 30 degrees.
grlsound reports that three, count them, EEs agree that the wye phase currents and wye phase voltages are out of phase by 30 degrees. This is should be obvious from the vector diagram.
Edit to remove the term balanced from the post.If we have a 30 degree shift between Vphase and Iphase, then the PF = cos(30) = 0.87. Then,
Preal = 2 x 10 x 120 x 0.87 = 2080W delivered by the transformer. PF in the load is 1.0.
No, I did not misquote, this is a cut and paste. And, he did not say it was a balanced delta either. It was a "single phase load, DELTA connected". The word "balanced" does not appear in the quote. If you continue to misread the text, you will never understand this. You appear to be sniping, trying to find some fault where none exists.Originally posted by bob:
rasttus posted
You have misquoted grlsound.Jim, let me quote from a post by grlsound:
"After consulting with not less than THREE electrical engineers, I think I may have a glimmer of an idea as to where, and why, one might use that elusive factor. This example is of a purely resistive single phase load, DELTA connected to a WYE source. (ie: transformer) I am told that when this connection happens, the current and voltage become out of phase by 30 degrees.
grlsound reports that three, count them, EEs agree that the wye phase currents and wye phase voltages are out of phase by 30 degrees. This is should be obvious from the vector diagram.
He reports that the engineers said with a balanced delta connected load the current and voltage is out of phase by 30 degrees. You then say that the wye phase current and wye phase voltage are out of phase by 30 degrees.
Neither of you are correct. In a balanced delta connected load the line current is sqrt of 3 x phase current and it is out of phase with the component phase current by
30 degrees. You can't have it both ways.
Originally posted by jim dungar:
My formulas work just as well with Z as with R. And yes I can imagine several possible real world load profiles that could unbalance a wye transformer as in your example.
Reply: Jim, of course they do. The point of the 12 Ohms @ 30 degrees to neutral is that this load provides the exact same current and phase as 20.8 Ohms @ 0 line to line. In one case the apparent power you calculate to be 2080VA, In the other it is 2400VA.
The same current through the same winding provides different apparent powers? How can this be? No one has answered this yet!
What does the phase angle between the current and the voltage have to do with calculating the VA loading of a transformer? The only affect I can visualize is the resultant neutral current. But the specific value of the neutral current does not come into play when analyzing the loading of each individual winding.
Reply: Nothing to do with apparent power, but it correlates real to apparent power.
2400VA x 0.87 = 2080W
And I can believe that there are at least three EEs that do not understand power relationships. Even as an EE myself, I would be out of my area of expertise in a discussion on electronics.
Reply: Jim this remark is unprofessional. Why don't you try to understand what is being said instead of criticizing people you do not know.
If you would work out the vector diagrams for this problem, I think you would see the light. Forget the standard formulas for the moment. Attack the problem from the basics.
Power is something taught in the old days, and a few of us have made the effort to retain this knowledge. I believe the EEs of today receive little or no schooling in AC circuits and power.
Now if someone has access to a circuit simulator, they could simulate this problem in seconds and see the various voltages, currents, and angles. I can't make my PSPICE work right, or I would do it myself.
Stiff, my thought is that apparent power is a convenient way to tally up loading without having to bother with power factor and separating the single phase and three phase loads. Don't know what the NEC says about it, but it was taught in the EE schools 50 years ago.Originally posted by hardworkingstiff:
Rattus,
What you have said makes perfect sense to me.
Didn't the NEC get away from "watts" and go to "VA" in order to make sure the conductors (and I would guess transformers) can handle the apparent power?