OK lets take a 75 KVA 480 /208-120 V 3PH transformer secondary is lets say phase conductors are 300KCML ALU with a 1/0 ALU supply side bonding jumper In each case we bond the neutral to metal ground inside the transformer the neutral or grounded conductor even if it is uncut a single conductor looping back down directly to metal case of transformer is not to code ?
The 1/0 is the supply side bonding jumper and we run that with the secondary phase & grounded conductor to the load or panel .
Please explain why if i use the grounded conductor and connect to the neutral bus with a lug in the transformer then without a splice pass it directly with a loop to the metal case were all grounds are connected inside the grounding electrode conductor building steel cold water . That it still needs supply side bonding jumper attached to metal case and to neutral bus inside transformer . Which in most cases is smaller than the grounded conductor ?
I think if you think of the supply side bonding jumper like an EGC, but sized as a GEC you might understand it better, because it is at or ahead of the disconnect on the secondaries of the transformer but does not create another parallel path between the grounded conductor and the panel case, it is basically an EGC sized to table 250.66, also the SSBJ can be a non-flexible metal raceway between the transformer and the panel as long as bonding bushings are installed.
Here is a equivalent service example of the SSBJ lets say you have a meter base with an isolated neutral terminal block that isolates the neutral from the meter case, also you have PVC between the meter and the main breaker panel, if you bonded the neutral in the panel you would then have to run a bonding jumper back to the meter and bond the case, this conductor would also have to be sized per table 250.66, but then you could also just bond the neutral at the meter and the panel so that is why we don't see it much.
So if you understand that if a metal raceway is installed between the transformer and first disconnect you can bond the neutral at the panel or at the disconnect but not both, then you must install a SSBJ from the point you bonded the neutral to the others case, if you have run PVC then you are allowed to bond the PVC at both the transformer and at the first disconnect or run a SSBJ between them.
The system bonding jumper is the same as the main bonding jumper for a service, if you have a main breaker panel fed from a transformer you can even use the screw it comes with as the system bonding jumper just like you do for a service, or you have to use a wire, but just like a service the GEC's must land with the neutral on the same bus bar because the screw would not be allowed in between 250.24.
If you have a install that is small enough that table 250.66 is not sizing the conductor over 3/0 then using the system bonding jumper to also feed out to the grounding electrode is fine, but if it is a larger install where the 12.5% comes into play it would not make sense to do this as the GEC stops at 3/0 but the system bonding jumper will be required to meet the 12.5%