jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
... The code still tells us to use the voltage ratio of the transformer, rather than the voltage ratio of an individual pair of windings.
...
Sorry, but you made that up. The code says "primary-to-secondary voltage ratio". That's the entire phrase. It's ambiguous as to whether that refers to windings or total assembly.
In my opinion a person is quite justified in interpreting it as the referring to the total assembly, because the code essentially never requires consideration of equipment internals, especially when not explicitly stated. It never even occured to me to think otherwise before this thread. But, nonetheless, the calculation result under that interpretation gives a different (lower) level of protection to the secondary conductors of a delta-wye than an wye-wye.