- Logan, Utah
Great Thread Chris......:smile: This is a tough section to interpret.![]()
It is a very tough section to interpret, that is why I though about starting this thread.
Chris
It's possible that, despite the #12, the box in pic 2 is for a switch, not a receptacle. If I'm correct, what are the opinions?
I agree, it is not as clear as it could be.:smile:
Yes, but I feel confident with how I called this item on the inspection report.![]()
I have always taken the position that if the receptacle is accessed from the bathtub then it is in the bathtub space.
I do see it your way but I can certainly understand Greg's view.:smile:
I do not agree with Rick's position.
Certainly a receptacle in a code legal position beside the tub could be accessed from in the tub.
Correct, this is a hydromassage bathtub not an indoor hot tub.
Chris
I do not understand logic in this code. If it is a spa or hot tub we would not allow the receptacle but hydro tub its safe ? Water not the same ?
Then the receptacle is allowed #1. Just no way i could call that shelf in the tub area. If it is then so is the toilet and sink. This section needs updated before we kill someone. I do not understand logic in this code. If it is a spa or hot tub we would not allow the receptacle but hydro tub its safe ? Water not the same ?
The biggest difference that I can see between a hydromassage bathtub and a spa or hot tub is that a hydromassage bathtub is designed to be drained after each use whereas a spa or hot tub stays filled for an extended time.
Chris
I have no idea and did not say I had one. What is yours? Look at 406.8(C) Bath Tub and Shower Space. Receptacles shall not be installed within or directly over a bath tub or shower stall......The point is this is open for interpretation. Two key words here "space and stall" See the problem?
in picture #2 why would it be any differant to install a 2x4 nailer, you move the receptacle off the edge of the tub by 1x1/2.
If the tub has a tile surround that lays right up to the lip of the tub, is this now in the tub space.
I personally would add the 2x4 or lay the recep horizontal in the back splash, but the fact is that recep could really only be 2 to 3'' from the tub.
but that it is code complaint IMHO
OK lets try it this way, just where do you think the tub space starts and ends ? Typical tub is 5' 0 " long ,about 32 inches wide and about 20 inches high. You tell us how many inches are tub area horizontally from edges of tub.
Could a vanity be in the tub area ?
Jim read the entire thread it is all about everyones IMHO. No one knows the answer to this section Number it has been proven with this thread.
Took me a while to get through all this to see where everyone's going--so far I don't know if anyone's going anywhere:roll:We had a challenge to an install, where the switches for the bathroom vanity, exhaust fan, recessed lighting, etc. were able to be reached from the tub while standing in it. The inspector (who had never failed a the exact same install before) dinged it. We got the definition, from some Illinois authority, saying that tub space is any space directly above the tub and its complete rim and/or bench, up to 8' above.
The switches stayed. FWIW, my reading of the code says that #1 is not in tub space, while #2 is a couple inches within the tub space. I don't like either one, and I've actually installed recepts. for tvs in 4 1/2 in alcoves similar to the one pictured, for flatscreens. IMO that alcove in #1 is big enough they could fit a TV, coffee maker, drink mixer, and more in it.