Yeah an AHJ or poco rep....my first thought is to come off those bottom double lugs into a disco tagged onto the whole shebang....~RJ~
Is this pedestal part of the utility transformer or is it a non-fused disconnect (power pedestal)?
If this is the service I'm thinking that the house is wrong haveing the neutral and ground bond at the main panel.
Is this house a mobile home?
This set up is odd enough that I wouldn't feel funny asking a few questions of the AHJ. They should of had an inspection when they turned power on for the house but things don't seem right to me.
Trying to think if neutral is normally insulated from can on normal meter.
Yeah an AHJ or poco rep....my first thought is to come off those bottom double lugs into a disco tagged onto the whole shebang....~RJ~
The neutral is not insulated from a normal meter can. I don't know if this one is or not.
The lock on the meter (seal) and maybe a barrel lock or other anti-theft/tamper lock would be normal.
Most of the power pedestals I have dealt with are in mobile home parks. Grounding and bonding are done at the pedestal . After that there is a feeder to the moble home (4 wire ). This is similar but probably supplied by the power company (green color ). You may have to give them a call.
Who makes that enclosure? Never seen one like it. With the green color it makes me think it's a utility transformer, meter, and transfer switch all-in-one??
Is that a transfer switch of some sort?
is that the neutral bar across the bottom? it appears to be bolted to the frame.
are the wires at the top coming from the meter?
Though you never see a pedestal type like OP has, we do have pole mount versions of that all over the place around here. They are not listed, the POCO provides them, and for less then a contractor can install a manual transfer switch in accordance with NEC. I have one at my place - was still cheaper then I can put in my own manual transfer switch in accordance with NEC.Could not find info on enclosure. Believe at this point it is Durham. Not exactly sure about transformer.
It is some sort of distribution point, but doesn't fit all criteria of site isolation device.
Sent from my iPhone using Tapatalk
Everything leaving that setup is still considered to be service conductors by all the inspectors around here.
That is my opinion also as I stated earlier. Power company trany so the wires to the garage are service conductors
Ok. I agree with that but wording through me for a loop for a minute, but practice says I've seen them installed three wire with no equipment ground. Guess I dig it up and do right. Thanks for all your input. It has been educational. If anyone has interpretation of the article with equipment ground bonded at distribution point I would be glad to hear.
Sent from my iPhone using Tapatalk
but mainly my pride of having to own up to it to the homeowner,
Put a breaker or fused disconnect out right on or adjacent to that pedestal - that becomes the service disconnect for the feeder to the shed. You can then use the already buried UF cable - will need to utilize the equipment grounding conductor though because it is a feeder. Before 2008 NEC you could have just run a grounded conductor and bond it at the second structure, but now you must run a separate EGC with such a feeder.