OK Guys and Gals: Here is the final word: ?True.? Here is why: 400.7(A)(8) and 400.8(B) (NEC 2002). Here?s the proof:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The under-counter light is an appliance.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">It is designed to be fastened in place in such a way as to permit ready removal for maintenance or repair.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">It is intended for flexible cord connection.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Therefore, per 400.7(A), it is permitted to be used with a flexible cord, even if it its screwed into the bottom of the counter.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Therefore, per 400.7(B), it is required to be energized from a receptacle outlet.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Nothing in the code puts any restriction on what may or may not be plugged into a receptacle outlet that is on the ?Small Appliance Circuit.? Besides, as I said above, the under-counter light is a ?small appliance.?</font>
<font size="2" face="Verdana, Helvetica, sans-serif">QED