True or false:
A cord and plug connected undercabinet task light can of course be plugged into a small appliance receptacle, but the same light can not be hardwired to the small appliance circuit?
Re: under-cabinet lights
True. BUT, I have no doubt that this group can find some way to twist this around so bad that there would be no answer that we could all agree on. :D Three replies, going for 300!
True.
On the same lines as :
You can plug a vaccum into a dining room receptacle but can you hard-wire a 120v. vac port off of the dining room circut?
Scott, after I stop laughing I might consider that a challenge. :D :D
At first read and before my first cup of coffee I think I will say false. After a little though I may change my mind but as it stands now I think I will stay with false.
Is this light permanently installed under this cabinet? Then we might have a problem and based on this I stand with false.
Can I install the sink light or the hood fan light and cord and plug them?
Had coffee, took shower, shaved and dressed for work.
Now to get serious about the under cabinet light that is permanently installed.
210.52 (B) Small Appliances. (2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.
Exception No. 1: A receptacle installed solely for the electrical supply to and support of an electric clock in any of the rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power for supplemental equipment and lighting on gas-fired ranges, ovens, or counter-mounted cooking units.
Don?t see any allowances for under cabinet lighting. If this light was not installed then there would be no problem but the fact that it is installed under the cabinet then the problem.
As outlined in the original post would be in violation of 210.52 (B) (2)
Electrofelon wrote:
...but the same light can not be hardwired to the small appliance circuit?
JW, slow down. The answer is "true." :D
By all rights, there are no other outlets in this kitchen, JW. (Edit: With the cord-connected light! :D
[ April 28, 2005, 07:57 AM: Message edited by: georgestolz ]
What I am saying is that if I can?t hard wire it to the small appliance circuit then I can?t permanently install it and then use a cord and plug and call it portable. If it is installed to the under side of the cabinet then its use is intended for task lighting and can not be used on the small appliance branch circuit per 210.52 (b) (2)
In my effort to see 300...
I think I agree with JW, that if it is a permanently attach piece of equipment, be it a light or a can opener or whatever, now it has to be wired appropriately. The canopener is an appliance. The U/C light is not.
As far as portability, there is nothing that says we can't plug an air freshener, a vacuum, a curling iron, a plug in search light or anything else into those outlets, but as soon as it becomes permanent, it has to be an appliance.
Only 280some to go...
OK Guys and Gals: Here is the final word: ?True.? Here is why: 400.7(A)(8) and 400.8(B) (NEC 2002). Here?s the proof:
</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">The under-counter light is an appliance.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">It is designed to be fastened in place in such a way as to permit ready removal for maintenance or repair.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">It is intended for flexible cord connection.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Therefore, per 400.7(A), it is permitted to be used with a flexible cord, even if it its screwed into the bottom of the counter.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Therefore, per 400.7(B), it is required to be energized from a receptacle outlet.</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Nothing in the code puts any restriction on what may or may not be plugged into a receptacle outlet that is on the ?Small Appliance Circuit.? Besides, as I said above, the under-counter light is a ?small appliance.?</font>
<font size="2" face="Verdana, Helvetica, sans-serif">QED :D
Charlie - talk about a s....t....r....e....t...c...h!!! I see nothing in 400.7 or 400.8 that indicates that an object becomes an appliance by installing a flexible cord. 400.7 lists items that can have flexible cords, nowhere does it say that item now becomes an appliance by doing so.
I think I'm going to agree with jw on this one; once you fasten the luminaire to the cabinet it becomes permenant and not allowed on the sm. appl. br. ckt.
As a 'by-the-way'... in Calif. those under cab lights will probably be going by the way-side come Oct. 1 when the new state Energy Code (2005) becomes effective.
Folks have been using those small fluor. fixtures under the cabs to meet the fluor. general lighting requirements (Energy Code) for years, in Oct. 1 that loop hole goes away and designers/electricians will have to supply the kitchen with flour. lighting for 50% of all wattage used for lighting in the kitchen.
Thanks for the heads up. I can't find the stupid energy code here anymore.
50% of the lighting in watts? That's bull! The people who write this stuff need phsyciatric elvauation. And pay cuts too, I'm sure.
So we're going to be on 2005 in October?
Originally posted by dana1028:I see nothing in 400.7 or 400.8 that indicates that an object becomes an appliance by installing a flexible cord.
I did not say that any NEC article caused the light to become designated as an "appliance." Nor did I say that it is the presence of a cord that causes the light to become designated as an "appliance." What I said is that the light is an "appliance."
From the realm of logical reasoning, this is called "begging the question." OK, so ya caught me. Ya gonna turn me over to the Logic Sheriff? :D
Charles B., we know you've made a logical faux pas, all we're asking for is a full confession and, I promise, the forum will go easy on you.