Re: under-cabinet lights
410.30 addresses the installation of the cord to the fixture and in no way addresses the installation of the fixture on a small appliance circuit. What is the point of injecting 410.30 in this debate?
The original post addresses using a small appliance circuit to supply a light fixture, so lets try to stay with this point in this debate.
Where I see a lot of confusion in this matter comes with the word ?receptacle? and the misunderstanding of just what this device is. It is an outlet, a place to receive current for a piece of equipment. When a piece of equipment is plugged into a receptacle it becomes an outlet for that piece of equipment. A good example of this would be found in 210.52 (F), ?at least one receptacle OUTLET shall be installed. The receptacle outlet described here is called ____?
I have made this statement; ?If a receptacle has a lamp plugged in it then at the point of plugging in the lamp that receptacle becomes a lighting outlet.
Then George asks, ?show me a reference to back that up. Unless there is some other section that modifies the definition of "lighting outlet", that statement is false.?
George the statement, ?a receptacle that has a light of any kind plugged into it becomes a lighting outlet? is true just as the receptacle that has a washing machine plugged into it is the laundry outlet.
The receptacle is an outlet and what ever is plugged into it will denote what the outlet is called. Most of the 15-ampere receptacles that are through out a house are referred to as general-purpose outlets.
This train of thought that a receptacle is not an outlet leads me to believe that the definition of receptacle outlet as found in article 100 should be eliminated.
A simple question about this under cabinet light that could clear things up is, when we finish using this light will it be put away like the mixer, vacuum cleaner and other appliances? If the answer is no it will remain attached to the under side of the cabinet then there is a problem.
410.30 addresses the installation of the cord to the fixture and in no way addresses the installation of the fixture on a small appliance circuit. What is the point of injecting 410.30 in this debate?
The original post addresses using a small appliance circuit to supply a light fixture, so lets try to stay with this point in this debate.
Where I see a lot of confusion in this matter comes with the word ?receptacle? and the misunderstanding of just what this device is. It is an outlet, a place to receive current for a piece of equipment. When a piece of equipment is plugged into a receptacle it becomes an outlet for that piece of equipment. A good example of this would be found in 210.52 (F), ?at least one receptacle OUTLET shall be installed. The receptacle outlet described here is called ____?
I have made this statement; ?If a receptacle has a lamp plugged in it then at the point of plugging in the lamp that receptacle becomes a lighting outlet.
Then George asks, ?show me a reference to back that up. Unless there is some other section that modifies the definition of "lighting outlet", that statement is false.?
George the statement, ?a receptacle that has a light of any kind plugged into it becomes a lighting outlet? is true just as the receptacle that has a washing machine plugged into it is the laundry outlet.
The receptacle is an outlet and what ever is plugged into it will denote what the outlet is called. Most of the 15-ampere receptacles that are through out a house are referred to as general-purpose outlets.
This train of thought that a receptacle is not an outlet leads me to believe that the definition of receptacle outlet as found in article 100 should be eliminated.
A simple question about this under cabinet light that could clear things up is, when we finish using this light will it be put away like the mixer, vacuum cleaner and other appliances? If the answer is no it will remain attached to the under side of the cabinet then there is a problem.