al hildenbrand
Senior Member
- Location
- Minnesota
- Occupation
- Electrical Contractor, Electrical Consultant, Electrical Engineer
Re: Ungrounded AFCI?
Hey Folks,
This thread has been an interesting read. Seems to me George is on to something. . .
250.130(C), when applied to an older installation, to me, requires that we think of a specific "general" installation or two.
Permit me to suggest two different single family dwellings, for our consideration. </font>
Every one sees these, if they do any amount of residential work in existing dwellings. There are a lot of them still in service, and likely to be so for decades to come.
The most common ground, in my experience, is a #8 copper running from the neutral bus to the closest metal cold water pipe. The water meter may, or may not, be jumpered. The cold water pipe is part of the GES all the way through the dwelling to the clamp holding the #8 copper GEC (grandfathered legal pre-1993 NEC).
Today, when I do the work that George lays out in his last diagram I connect the EGC for "New #1, #2 & #3" to the first 5 feet of water pipe (as per today's NEC).
When the dwelling water system is upgraded, who's to tell me that the plastic pipe (above the ceiling, hidden) separating the water pipe into two pieces is, in fact there?
The water service tests grounded, especially on a municipal metal system, but also on a well.
And the service center neutral tests grounded through the service grounded conductor to the transformer ground. Yet, in the example of a private well water system, the only thing connecting the two metal halves of a plastic separated water pipe GES is the earth itself.
Edit to get the UBB code right...
[ July 07, 2005, 12:53 AM: Message edited by: al hildenbrand ]
Hey Folks,
This thread has been an interesting read. Seems to me George is on to something. . .
250.130(C), when applied to an older installation, to me, requires that we think of a specific "general" installation or two.
Permit me to suggest two different single family dwellings, for our consideration. </font>
- <font size="2" face="Verdana, Helvetica, sans-serif">A detached 1955 single family dwelling on a private well water system with an existing 120/240 V 60 A fused service center.</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">A detached 1955 single family dwelling on a metal municipal water system with an existing 120/240 V 60 A fused service center.</font>
Every one sees these, if they do any amount of residential work in existing dwellings. There are a lot of them still in service, and likely to be so for decades to come.
The most common ground, in my experience, is a #8 copper running from the neutral bus to the closest metal cold water pipe. The water meter may, or may not, be jumpered. The cold water pipe is part of the GES all the way through the dwelling to the clamp holding the #8 copper GEC (grandfathered legal pre-1993 NEC).
Today, when I do the work that George lays out in his last diagram I connect the EGC for "New #1, #2 & #3" to the first 5 feet of water pipe (as per today's NEC).
When the dwelling water system is upgraded, who's to tell me that the plastic pipe (above the ceiling, hidden) separating the water pipe into two pieces is, in fact there?
The water service tests grounded, especially on a municipal metal system, but also on a well.
And the service center neutral tests grounded through the service grounded conductor to the transformer ground. Yet, in the example of a private well water system, the only thing connecting the two metal halves of a plastic separated water pipe GES is the earth itself.
Edit to get the UBB code right...
[ July 07, 2005, 12:53 AM: Message edited by: al hildenbrand ]