Originally posted by don_resqcapt19:
There is no code compliant method of installing a receptacle in a new location, unless you provide an EGC to that receptacle.
Don
Edit: I don't believe that's completely accurate.
Part VII lays out the "method" of "grounding" equipment (which we know to be "bonding", despite it's misnomer). Immediately a general statement is made, as to where EGC's are to ultimately terminate, for ungrounded and grounded systems.
The last part of the general 250.130 (before the (A) states:
For replacement of non-grounding-type receptacles with grounding-type receptacles and for branch-circuit extensions only in existing installations that do not have an equipment grounding conductor in the branch circuit, connections shall be permitted as indicated in 250.130(C).
(C) repeats this:
(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions. The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following: ...
As JW pointed out, this is
permissive language. If you had to use one of the items in the list, then it would state "
shall be connected to one of the following."
Then, to be tidy and helpful, the FPN steers you to 406.3, which states:
(B) To Be Grounded. Receptacles and cord connectors that have grounding contacts shall have those contacts effectively grounded.
At this stage, all receptacles are to be grounded. How are we to do this? Recipe:
(C) Methods of Grounding. The grounding contacts of receptacles and cord connectors shall be grounded by connection to the equipment grounding conductor of the circuit supplying the receptacle or cord connector.
The branch-circuit wiring method shall include or provide an equipment-grounding conductor to which the grounding contacts of the receptacle or cord connector shall be connected.
Uh-oh. We're in trouble. The branch circuit we are going to use to replace receptacles, or add a new receptacle with, has no EGC. We're screwed. Oh, wait:
FPN No. 2: For extensions of existing branch circuits, see 250.130.
So, at this stage, before any other remedies are presented, we get an FPN suggestion to peek back at 250.130.
(3) Nongrounding-Type Receptacles. Where grounding means does not exist in the receptacle enclosure, the installation shall comply with (a), (b), or (c).
We are dealing with a circuit bearing non-grounding type receptacles. No EGC was originally installed with the BC conductors.
Then, twice, once in (b) and once in (c), this statement is made:
...An equipment grounding conductor shall not be connected between the grounding-type receptacles.
Why would an original circuit with no EGC suddenly grow one between receptacles? Because someone extended the circuit with new methods that brought an "EGC" with them. This is dangerous; isolating each non-grounding GFI-protected receptacle is safer than exposing the
entire new addition to current that cannot be faulted, so it's required to be isolated.