Originally posted by jwelectric:
George you drawing is noncompliant to start with.
250.50 Grounding Electrode System.
All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present at each building or structure served shall be bonded together to form the grounding electrode system.
This was true in 1975 as stated in 250-80 of that cycle and in 250-81 we were told that a metal underground water pipe SHALL be used as the grounding electrode.
The grounding electrodes in my diagram are bonded together in the MDP Panel. In 1960, it was installed to code, if not beyond code.
250-112 is quoted below as to how we were to connect to this water pipe.
1975 cycle page 102 article 250 section 112
To Grounding Electrode. The grounding connection of a grounding conductor to a grounding electrode shall be made at a point and in a manner that will assure a permanent and effective ground. Where necessary to assure this for a metal piping system used as a grounding electrode, effective bonding shall be provided around insulated joints and sections and around any equipment that is likely to be disconnected for repairs or replacement.
The 1975 cycle is as far back as I have at this time but I am always looking for older issues of the NEC.
And in 1960, there were no insulating joints or sections. In 1982 a pipe in the basement burst because the occupants went on an extended vacation and forgot to turn the furnace on. The pipe burst and was repaired with PVC by a plumber with no electrician staring over his shoulder in 1982.
The basement was finished in 1985, and no notice was given to another piece of pipe in an old house.
When I got into the electrical trade a year or ten before this cycle we used the water pipe and attached as close to the entry point as possible on all jobs we done.
That's great. I do things
beyond code all the time, but I don't expect to see it in old work.
Sparky should make sure that the water pipe is bonded to the grounded (neutral) at the service before leaving this job.
Why? He attached it to a 2005-defined grounding electrode, which is all that 250.130 (and 250.50) require him to do.
Do 75% of electricians even know the difference between grounding and bonding?
Great, some of us here are smart enough to know better. But a lot of us aren't. We follow the code. If the code is incomplete, how are we to be held liable?
In (an unrelated) basement I was in recently, and DIY'er had connected the grounding screw of a receptacle to a water pipe with a chunk of THHN. If it weren't for the 5' rule today, it would be legal (aside from the obligatory electrical tape water clamp
). Fifteen years ago it would have been legal.
Why connect it to a grounding electrode? It's completely misleading. It further muddies the already murky concepts of grounding
versus bonding.