Re: Ungrounded AFCI?
Here's the logical progression as I see it.
Assume that circuit extension includes a new receptacle installation.
Logical items with reference numbers for ease of disagreement:
[1] 250.130. When installing a receptacle where the branch has no EGC the second half of the paragraph grants specific permission to install under 250.130(C).
[2] The phrase "shall be permitted" is used. That means that if the NEC says something contradictory somewhere else, then the NEC is neurotic, and it's still permitted.
[3] 250.130(C) Blah, Blah, Blah, "shall be permitted" to be connected to any of the following. The following being 250.130(C) (1) through (5).
[4] 250.130(C)(1) says I can connect anywhere on the grounding electrode system that's described in 250.50. And it's a good thing it says that because there's no definition for a grounding electrode system in article 100. But even if there were I "shall be permitted" to use the description in 250.
[5] 250.50 describes the grounding electrode system as what most of us know it to be. It doesn't describe it to be connected to anything. (Outside of it's own electrodes)
[6] I've now run out of code requirements related to the EGC of this new receptacle and as far as I can tell I have specific permission to install it with an EGC that connects to only ground electrodes.
The same argument can be made for 250.130(C)(2). But less effectively because the definition for grounding electrode conductor does a slightly better job (not saying much) of putting the EGC on the service neutral.
I'm not taking sides or having preferences or giggling uncontrollably,
just reading the code.