So is it allowed on the kitchen small appliance branch circuit.
Last edited:
I'm not saying it is a single receptacle (refer to receptacle definition)....
To say that this is only a single 15 amp receptacle connected to the circuit is to say that the USB circuity is not connected at all.
Well then it is not a single receptacle just like a 15 amp duplex is not a single receptacle and it can be on a 20 amp circuit with no additional outlets.I'm not saying it is a single receptacle (refer to receptacle definition).
What I am saying is that it is only one receptacle, rated 15A, and only one outlet on the 20A branch circuit, as described in the OP. What part of 210.21(B) does this comply with?
One outlet. What device or utilization equipment is connected at the outlet matters not.One outlet with two utilization points, or two different outlets? They are on one yoke or strap but they definitely are not the same type of utilization points.
IMO yes.Should they be allowed on a small appliance branch circuit?
No... but I don't believe you can count a receptacle AND the outlet it is connected to as two.210.21(B)(3) for two or more receptacles or outlets. Are you saying that you cannot have one of each type to comply?
Question for all, is one 15A-rated duplex receptacle permitted on a 20A branch circuit? Is it one or two receptacles?
No... but I don't believe you can count a receptacle AND the outlet it is connected to as two.
I agree.Yes, and a duplex is considered 2 receptacles
Just as a duplex receptacle is considered 2 receptacles why wouldn't this device be considered as 2- not 2 receptacles but a recep. and another outlet.
I agree.
So let's say we have an illuminated switch-receptacle combo device, rated 15A 120V, switch controls the receptacle, installed in a 1G box that is the only outlet on a 20A circuit. Is this permitted? ...and if yes, under what provision?
Take the device out of the box. You have an outlet. Put it back in, you still have an outlet with a device. I don't believe 210.21(B)(3) intends for the outlet and a receptacle device installed in that outlet to be counted as meeting the "two or more" requirement.Just as a duplex receptacle is considered 2 receptacles why wouldn't this device be considered as 2- not 2 receptacles but a recep. and another outlet.
Okay... but where does Code say you can have one 15A-rated receptacle on a 20A branch circuit?
I agree about the intent as I stated a few times however we cannot go by intent.Take the device out of the box. You have an outlet. Put it back in, you still have an outlet with a device. I don't believe 210.21(B)(3) intends for the outlet and a receptacle device installed in that outlet to be counted as meeting the "two or more" requirement.
Not sure I follow. If a single recep. is fed by a 20 amp circuit then yes it would need to be 20 amp. You know that so I am missing something. I assume you mean single recep when you say simplex.What about a 15A simplex receptacle being the only connection in the only outlet box of a 20A branch circuit. Are you going qualify that as "two or more".
Same argument as your OP.This is the same argument. IMO, it should be a 20 amp circuit however based on code I believe a 15 amp circuit would be compliant. Get rid of the light---that changes things. Now why would a lighted switch change anything-- it really shouldn't.
Take the device out of the box. You have an outlet. Put it back in, you still have an outlet with a device. I don't believe 210.21(B)(3) intends for the outlet and a receptacle device installed in that outlet to be counted as meeting the "two or more" requirement.
What about a 15A simplex receptacle being the only connection in the only outlet box of a 20A branch circuit. Are you going qualify that as "two or more".
What I'm saying is you don't count the "assembly" as one receptacle AND one outlet to qualify as "two or more receptacles or outlets", do you?...
Not sure I follow. If a single recep. is fed by a 20 amp circuit then yes it would need to be 20 amp. You know that so I am missing something. I assume you mean single recep when you say simplex.