Re: Using neutral as a traveller on 3way switch
Hey guys,
Sometimes you can't see the forest for the trees. I think this topic has been over-analyzed.
Article 200.6(A) States that you
CANNOT mark a conductor as a
grounded conductor if it is
6 AWG or smaller. There are 4 exceptions to this :
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The grounded conductor of mineral-insulated, metal sheathed cable may be identified at the time of installation by distinctive markings at its terminations</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">A single-conductor sunlight-resistant outdoor-rated cable used as a grounded conductor in photovoltanic power systems as permitted by 690.31 shall be identified at the time of installation by distinctive white markings at all terminations.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Fixture wire shall comply with the requirements for grounded conductor identification as specified in 402.8.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">For aerial cable, the identification shall be as above, or by means of a ridge located on the exterior of the cable so as to identify it.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
The code is placing requirements on the conductors used as a Grounded conductor. If a white conductor is used elsewhere as a phase conductor, then it must be re-marked!!!
The code also states in article 200.7 the a conductor of a white gray color or with three continuous white stripes may only be used as a grounded conductor except as permitted in 200.7(B) and (C).
In 200.7(C)(2), the code makes an exception for using these conductors as a phase conductor for single-pole, 3-way, or 4-way switch loops and states the requirements for remarking the conductors.
Anyone see this any different????