Re: Using neutral as a traveller on 3way switch
Thanks for the response, Goldstar. I agree that the question in this thread is ultimately "
whether white wires can be re-identified when used as travelers".
I suspect that the confusion around the language used in 200.7(c)(2) comes from mental substitutions for the exact words used. Your description of re-identifying the white conductor in the 14-2 switch loop is, perhaps, just such a case.
Answering my own question: The conductor running from the OCPD, the 15 or 20 amp circuit breaker marked "SWD", through the fluorescent luminaire J-box and down to the wall mounted toggle switch
is a conductor between two single pole switches.
It is easy to see this conductor is
used for the supply to the switch. After all, it's the branch circuit hot conductor. . .right? But the breaker is listed as a switch. From the White Book:
Switching Type--
Circuit breakers marked "SWD" are suitable for switching 120, 277 or 347 volt fluorescent lighting on a regular basis at the rated voltage.
This "SWD" breaker is not a special breaker. Virtually all commodity single pole 15 and 20 amp circuit breakers are listed Type SWD.
So, the conductor beginning at the breaker and ending at the wall mounted toggle switch is between two switches. Looks like a "traveller" to me. A traveller is a conductor connected on either end to a switch.
So, do we make 14-2 and 12-2 NM switch loops a violation of the NEC? No, because the re-identified white wire ends at a switch, thereby supplying the switch that it ends at. The wire that connects to the switch on one end and connects to the luminaire on the other end has to be black because it is
200.7(c)(2)
a return conductor from the switch to the switched outlet.
A traveller is connected to a switch on both ends. No luminaire. A traveller cannot be
200.7(c)(2)
a return conductor from the switch to the switched outlet.
because it doesn't end at the switched outlet.