dnem said:What he’s trying to say [without actually saying it] is that on motors the wire size and the OCPD size is speced separately on the nameplate.
David I agree with you and I think the rest do as well.
The problem is it seems Gmack is saying that applies to receptacles as well.
Gmack said:abbattista said:NO! You cannot protect a 15A receptacle with a 30A CB under any circumstances.
In Article 430 it is acceptable and preferable.
In other words a 15 amp outlet supplying a motor could be protected with a 30 amp breaker.
I disagree with that idea if that is what he was trying to say.