Using THHN No. 14 on 20 Amp lighting circuit

Status
Not open for further replies.
dnem said:
What he’s trying to say [without actually saying it] is that on motors the wire size and the OCPD size is speced separately on the nameplate.

David I agree with you and I think the rest do as well.

The problem is it seems Gmack is saying that applies to receptacles as well.

Gmack said:
abbattista said:
NO! You cannot protect a 15A receptacle with a 30A CB under any circumstances.

In Article 430 it is acceptable and preferable.

In other words a 15 amp outlet supplying a motor could be protected with a 30 amp breaker.

I disagree with that idea if that is what he was trying to say.
 
iwire said:
David I agree with you and I think the rest do as well.

The problem is it seems Gmack is saying that applies to receptacles as well.



In other words a 15 amp outlet supplying a motor could be protected with a 30 amp breaker.

I disagree with that idea if that is what he was trying to say.

Me too.That would leave a receptacle that might get used for something else that is not qualified.
 
Even if the motor receptacle were an oddball configuration for the structure, which was not a standard 15A configuration, I do not see how installing it on a 30A breaker would be legal? That seems to be against both 210.21(B)(1) and (3).
 
I agree as well and so does 430.42, specifically 430.32(C)

Roger
 