So I have been reading a few of these forums trying to get an understanding for how to run the voltage drop calcs for an unbalanced lighting run on 480/277v 4-wire line-to-neutral runs. I just haven't been able to grasp the concept of what to do. I am having trouble determining calculate the voltage drop to determine the wire size.
So I have 3 lighting runs.
Here is the image of the run to better visualize it:
And a PF of 0.9 was applied as well. Here is the Panel:
I appreciate any guidance you can give and any time you take to explain this to my very dumb brain.
So I have 3 lighting runs.
- Phase A has 3-300W fixtures spaced every 600 ft starting 600 ft from the meter
- Phase B has 2-300W fixtures spaced every 600 ft starting 1200 ft from the meter
- Phase C has 2-300W fixtures spaced every 600 ft starting 1800 ft from the meter
Here is the image of the run to better visualize it:
And a PF of 0.9 was applied as well. Here is the Panel:
I appreciate any guidance you can give and any time you take to explain this to my very dumb brain.