I agree with the first paragraph, but I would imagine one would boost the voltage at the source with a BB, not at the load.If you have a 30 volt voltage drop at 120v with lets say 10 amps of load, lets say a 3 watt timer, and a 1250 watt motor, so your voltage has dropped to 90 volts, now you use a BB to do a 32 volt boost, so you now have 122 volts with both loads running, let the motor turn off, and your timer will see 152 volts. Not good.
The BB will boost what ever voltage that is fed into it, by the adder voltage, so if you are trying to over come a voltage drop, the input voltage to the BB will rise as the load gets less.
I'm inclined to go with the new meter ped option if there is already 120/240 nearby.In my opinion, the two idea to consider are the PV-and-battery and the two-transformer step-up/step-down methods.
Here's a crazy idea, put the time clock where the power is and run a water line 2800'.
Call me crazy, but I was thinking a battery and solar charger.
If you have a 30 volt voltage drop at 120v with lets say 10 amps of load, lets say a 3 watt timer, and a 1250 watt motor, so your voltage has dropped to 90 volts, now you use a BB to do a 32 volt boost, so you now have 122 volts with both loads running, let the motor turn off, and your timer will see 152 volts. Not good.
The BB will boost what ever voltage that is fed into it, by the adder voltage, so if you are trying to over come a voltage drop, the input voltage to the BB will rise as the load gets less.
I agree with the first paragraph, but I would imagine one would boost the voltage at the source with a BB, not at the load.
In my opinion, the two idea to consider are the PV-and-battery and the two-transformer step-up/step-down methods.
Anyone got schematics of the step-up xformer compared to the bb? I don't follow why it's the way it is..
Thx
Jason
So it's only a big deal here because the load is fluctuating so much, right? Step it way up and it won't fluctuate much at all...gotcha
Not exactly
lets say you have a 20 amp load at 120 volts, you step it up to 480, now it's only a 5 amp load, at the other end you step it back down to 120 volts, your back to 20 amp at 120 volts but now you only have 5 amps on the long run wires so the voltage drop is less.
Power companys do this all the time. but at much higher voltages![]()
Vary the voltage into any transformer and it will vary the output right?
With voltage drop the voltage at the end of the line will vary in proportion to the current being drawn ok
now install any type of transformer that brings a voltage drop back up to nominal voltage and as long as the load stays the same it will be ok, but have the load turn off like in my example, and the voltage will rise proportionally to the current. thus allowing a higher voltage then expected.
I absolutely agree with that, but here's the difference: when you use a BB to boost, the power for the extra voltage is seen as extra line-side current, which adds to the voltage drop.with voltage drop, it doesn't matter which end you boost from, when the load turns off the voltage will rise to what ever is fed in at the start of the conductors.![]()