Dears,
I am involved in a Load Flow analysis with ETAP; for that purpose I have included in the model the transformers, switchgear, static and rotative loads and cables.
The 3ph cable sections selected is by means of ampacity and voltage drop calculation by means of the following formula;
Vd = sqrt(3) * L/1000 * I * (R*cosPHI + X*senPHI), being cosPHI=Power Factor. The criteria is not to reach to the 2% voltage drop from switchgear to MCC/Panel; and 3% from MCC/Panel to the end-load.
The case is that after performing the Load Flow study (considering the worst case) the values of voltage drops in the ETAP are very very different spreaded by the formula. :?
So my conclusion is that the sections of long tracks could be lower but this would not comply with formula!! :happysad:
I would like to know if someone could help me to understand why this is happening. Thank you in advance
FYI: already checked are the cable length, Resistance and Reactance to be the same in ETAP and in formula (L, R and X). Results:
Trafo with tapchanger => switchgear => MCC => static & rotatory loads
I am involved in a Load Flow analysis with ETAP; for that purpose I have included in the model the transformers, switchgear, static and rotative loads and cables.
The 3ph cable sections selected is by means of ampacity and voltage drop calculation by means of the following formula;
Vd = sqrt(3) * L/1000 * I * (R*cosPHI + X*senPHI), being cosPHI=Power Factor. The criteria is not to reach to the 2% voltage drop from switchgear to MCC/Panel; and 3% from MCC/Panel to the end-load.
The case is that after performing the Load Flow study (considering the worst case) the values of voltage drops in the ETAP are very very different spreaded by the formula. :?
So my conclusion is that the sections of long tracks could be lower but this would not comply with formula!! :happysad:
I would like to know if someone could help me to understand why this is happening. Thank you in advance
FYI: already checked are the cable length, Resistance and Reactance to be the same in ETAP and in formula (L, R and X). Results:
Trafo with tapchanger => switchgear => MCC => static & rotatory loads
- VD at MCC by Formula: 1.44%
- VD at MCC by ETAP (V=100% at switchgear) = 0,55%
- VD at MCC by ETAP (V=90% at switchgear) = 0,88%