Hi, I am having a problem of unbalanced strange values of system voltages in of our power generation plant,
the disturbance in voltage is being reflected on Low voltage side only,
system diagram is attached.
View attachment 20244
what the system must show at low voltage side is;
1. P-P 480V
2.P-N 277V
but the current scenario on delta side of transformer is;
L1-L2= 316 V
L2-L3= 147 V
L3-L1= 221 V
L1-N= 594 V
L2-N= 599 V
L3-N= 530 V
neutral is kept floating on both sides, i.e. both LV & MV neutral is floating.
is there any fault in on of the system phases?