Over voltage is phase to neutral, no phase to phase over voltage. Correct?both cases, whether connected or not, over voltages are present at bus , i just connected it to ground as routine practice
Over voltage is phase to neutral, no phase to phase over voltage. Correct?both cases, whether connected or not, over voltages are present at bus , i just connected it to ground as routine practice
Over voltage is phase to neutral, no phase to phase over voltage. Correct?
Over voltage is phase to neutral, no phase to phase over voltage. Correct?
Ingeniur: the OP says the neutral conductor to controller is grounded. Then how over voltage damage to the controllers?
In continuation of the above question, here is another question. mrmuneeb, is the transformer, you use for sensing the voltage, connected on the MV side phase to neutral or phase to phase?
In continuation of the above question, here is another question. mrmuneeb, is the transformer, you use for sensing the voltage, connected on the MV side phase to neutral or phase to phase?
for sensing, we are not using anything extra, same power transformer is being used also for voltage sensing to which we are feeding power from generator.
as of phase to phase voltages, i have one phase at higher voltage,
check video below;
https://youtu.be/hsPc9VpYDXU
mrmuneeb, why can't you automatically isolate the controllers also when both the engines i.e the generators are tripped, thereby avoiding over voltage damage to the controllers?
yes sir, they can be isolated automatically, but to sync again we need to connect to bus, and connecting again will cause damage as bus voltages remains high, we have to switch off the main Ring unit that is feeding to the client in order to sync additional engine.
engine needs bus sensing before closing on to bus.
on each pair(as shown in previous diagram) there must be one engine closed onto bus in order to sync the 2nd generator on the same transformer.
issue is on client side and is phase to ground, also seems to me that its location is far from our power plant, residential loads, distributed over a huge area.
When the two engines i.e the two generators are off, there is back feeding of power from MV side. Due to grounding of one phase (B phase in your case), the voltages are not balanced and as a result, there is over voltage in the LV bus damaging the controllers. So the first thing you have to do is to trace the ground fault in B phase and rectify. For that, why can't you engage a specialized agency to trace and rectify the ground fault in B phase?
Your MV supply is ungrounded. It may terminate on a MV-LV transformer with secondary grounded for supplying power to the client. If it is so, the client is not responsible for the subject ground fault unless the ground fault is on the primary side of MV-LV transformer and the client owns it.as the fault is on client end so we have informed client, but to prove that its on client end i am looking for a valid reason/proof.
i only have following reason "opening the main ring switch to client makes system normal"
for that client is arguing "why your main ring switch not tripping if there is any earth fault?"
however our main ring switch is set at 10% for 51(ANSI) & 50% for 50N(ANSI) these are the lowest possible settings for that ring main switch.
Your MV supply is ungrounded. It may terminate on a MV-LV transformer with secondary grounded for supplying power to the client. If it is so, the client is not responsible for the subject ground fault unless the ground fault is on the primary side of MV-LV transformer and the client owns it.
Fine. Then check if there is any ground fault in MV B phase up to ring main by disconnecting it and meggaring taking all precautions. That way you can prove the ground fault is on client side. Also note 51and 50N would not operate for such faults.yes, the client owns the MV-LV transformers at the distribution & the transmission lines as well.
our scope is only up to the main ring unit that is located inside our facility.
Fine. Then check if there is any ground fault in MV B phase up to ring main by disconnecting it and meggaring taking all precautions. That way you can prove the ground fault is on client side. Also note 51and 50N would not operate for such faults.
as the fault is on client end so we have informed client, but to prove that its on client end i am looking for a valid reason/proof.
i only have following reason "opening the main ring switch to client makes system normal"
for that client is arguing "why your main ring switch not tripping if there is any earth fault?"
however our main ring switch is set at 10% for 51(ANSI) & 50% for 50N(ANSI) these are the lowest possible settings for that ring main switch.
Provide ground fault alarm/ indication for each phase on MV side as it is an ungrounded power system.I see, so what type of protection is required for such faults