the way I read it
if mv and gen are grounded and a gen is off system goes down
if only gen is grounded he is good
if both gens in a pair are running he is ok
if one is running he is ok
if both are off bus v goes high ~800-1200
if mv and gen are grounded and a gen is off system goes down(some are off and some on, depending on load)
if only gen is grounded he is good (no sir, high bus voltage still remains on bus sensing lines of off engines)
if both gens in a pair are running he is ok (yes Sir)
if one is running he is ok (yes Sir, as soon as this one trips, its bus voltage also goes high, sensing input of controller gets damaged)
if both are off bus v goes high ~800-1200 (yes Sir)
it seems to me that engines that are running absorbs that high voltage, because as soon as we open the main MV circuit breaker that is feeding power to client everything gets normal, no high voltage, no unbalanced voltage.
i suspect any line to ground fault present far away on transmission lines.
since govt is evacuating the homes and cutting power to homes, the lines are not that managed after disconnection in that area.