mbrooke
Batteries Included
- United States
- Technician
:lol::lol::lol::thumbsup: Painful yet funny.
That is what the drawing cites, yes.Let me read that...
EDIT, is this it?
The difference is that the outbuilding us NOT being fed from the service. The building is being fed by an SDS and the loads inside the building are fed from a second SDS.So this skips as an outbuilding? I remember older codes allowed this, but I am sure new additions of the NEC do not...?
Yes, that is the key. That is why the exception is called out on the drawing (250.30(A)(1) Exception 2), as most think at first glance this is not a compliant installation. PVC conduit (no metallic path). This way you only need 2 conductors for the long 600 volt conductors. Makes for a very efficient use of conductor. Safe and code compliant.Continued....
Not sure where or if it is in [2011] or earlier. but the use of the grounded conductor only in the feeder to the outbuilding is, as called out on the diagram, allowed by 250.30(A)(1) in the [2014] code specifically when an SDS is used.
Whether the second transformer is in/on the building or separate from it (pad or pole mount), the feeder to the building is not electrically continuous with the original service.
A good point to consider!Correct, however there will be at least a 10 to 15 volt drop across the grounded conductor which will transfer into the structure. 15 volts while standing outside on earth can become a problem.
It would not transfer into the structure if the *second* transformer used only the local GES and did not have a connection to the long neutral.
Not quite as in the diagram, but acceptable I think.
Worst case make the long link ungrounded with a ground sensor.
Maybe....
Perhaps, but the long feed does not have a neutral and need not have a grounded conductor either.But would that be to code? Dont all incoming neutrals need to be bonded to the system?
You could consider this as a possible economical solution:
I did the math, assuming 120/240, unity power factor and 50 amps of balanced load (little to no neutral current), I would need 600 kcmil copper to have 3% voltage drop or 750 kcmil for a 3.5% voltage drop. Pulling this 4,000 feet will be a new one.
At a full 80 amps the voltage drop is 4.7%, but I would call this exceptable since a full 80amps of load is will not be common or continuous.
One the other hand going 600 volts I can use 1/0 copper or 3/0 AL assuming 20amps of current (50 on the 120/240 secondary)
1000 volts will let me use #4 cu at a 2.6% voltage drop, #6 for a 4% drop and #2AL for a 2.7% drop.
There is a difference between 1000 and 600 volt when it comes to cable savings.
The difference between 600 volts and 1000 volts is going to minimal as far as wire size. Going with 600 volts will allow you to use off the shelf equipment (transformers, panels, disconnects) and standard THWN or XHHW wire. Going with 1000 volts will require custom special order equipment and more expensive medium voltage wire. You will also have additional cost for terminating the medium voltage.
I would guess the bump from 600 to 1000 will add a substantial cost to the project.
Another thing to consider is future repair. If the transformers fail or get damaged the customer is going to be without power for an extended time while new equipment is built. 600 volts transformers and distribution equipment are stock items.
+1 on all of that....
and the nod goes to the voice of reason from san jose.....
575 volts is off the shelf on most of this.... you'll have
to get someone to make up the transformers, as they
are not really used much in the US, but i'd bet it adds
maybe 20% to the cost of the transformers, tapping them
at 575 instead of 480.... everything else is just toss it together,
and you are done.
and 1,000 volts makes it into a bastard thing, and what
you are going to save in reduced wire size will disappear
like the morning mist when you upgrade the wire insulation, and
get specially wound transformers that don't exist anywhere.
stuff made out of unobtanium is more expensive, generally speaking.
Maybe. Going to 2 KV saves dramatically on wire. Say we are talking single phase, 20kva, 3% VD. At 2KV, #8 copper will do it. 1KV/2KV PV wire is about 50% more than THHN, so two 4000' runs would be $4440. At 600V you would need 500 AL which, extrapolating from the last time I priced 250, would be $2/ft so $16000 for the 600V option. That is a lot and it doesnt figure increased labor and conduit costs.
If you want the long feed to be just two conductors, with no EGC or bonding jumper, then I think it needs to have a grounded conductor. 250.30(A)(2) requires a supply-side bonding jumper be installed with the circuit conductors, with the following exception:Perhaps, but the long feed does not have a neutral and need not have a grounded conductor either.
As shown in the image in post 49. That post makes me have to take back some of what I said in post 33 on running medium voltage but needing a third conductor for equipment grounding - but you can not have other conductive paths between the two structures either, shield on a telephone cable could get you if you have this, or a metal piping system between them.One option I heard and researched today is buying two 10kva pad-mounts and interconnect them via URD concentric neutral cable. Only issue is I have no idea how to make that NEC complaint.
Still don't know if cost will be less then larger low voltage conductors/cables. Don't know how much a 2.4 or 7.2 padmount would cost, guessing both are common enough they would be in same price range as POCO's use a lot of them. Next item that a POCO would not typically need is a disconnect (on the meduim voltage line) at the second structure, my guess is they cost just a little more then a typical 240 volt 100 amp safety switch.