Proposal 5-200 for the 1996 code.
5-200- (250-81): Accept
SUBMITTER: William E Laldler, Hanover, MA
RECOMMENDATION: Revise the second sentence as follows:
"Interior metal water piping located more than 5 feet (1.52m) from the point of entrance to the building shall not be used as a
the grounding electrode system or as a conductor to interconnect electrodes that are part of the ~,rounding electrode system."
SUBSTANTIATION: This new requirement in the 1993 code is being interpreted differently by code users. The new words will
clarify the intent as I understand it from the 1993 TCR and TCD.
That is, that the portion of interior water piping systems beyond 5 ft. is not considered reliable because of potential changes to the water
system that could involve the use of PVC piping.
PANEL ACTION: Accept.
PANEL STATEMENT: For further information on grounding electrode conductor connections to the grounding electrode system, see the panel action and panel statement on Proposal 5-190.
NUMBER OF PANEL MEMBERS ELIGIBLE TO VOTE: 12
VOTE ON PANEL ACTION:
AFFIRMATIVE: 11
NOT RETURNED: Shift