- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
I tried to specify a similar item as the main on what I intended to be essentially an MLO lighting panel. I had a 100 amp cable tap riser fed via a 100 amp breaker, with a 100 amp panel on every other floor. I didn't need a main breaker on each panel, but I wanted some way to turn off the panel locally, without having to take out the entire riser. So I called for a "main switch," describing it as essentially a main breaker, but with the overcurrent "guts" removed. The panel manufacturer's representative said they could do that, but they took credit for the overcurrent aspects of the main breaker as part of their panel's fault current rating. So I couldn't get the fault rating I wanted, without either going with a main breaker, or using a standard MLO panel. I wound up deleting the "main switch" requirement, using a MLO panel, and putting a non-fused disconnect switch upstream, to allow for local isolation. Live and learn. :roll: