what method --driving ground rods?
(G) Rod and Pipe Electrodes. The electrode shall be installed
such that at least 2.44 m (8 ft) of length is in contact
with the soil. It shall be driven to a depth of not less than
2.44 m (8 ft) except that, where rock bottom is encountered,
the electrode shall be driven at an oblique angle not
to exceed 45 degrees from the vertical or, where rock bottom
is encountered
at an angle up to 45 degrees, the electrode
shall be permitted to be buried in a trench that is at
least 750 mm (30 in.) deep. The upper end of the electrode
shall be flush with or below ground level unless the aboveground
end and the grounding electrode conductor attachment
are protected against physical damage as specified in
250.10.
so the GRVAD is a fully necessary item at times.
Not if you have an Al. An Al is an acceptable replacement for a GRVAD.
is encountered
250.10.
I pity the fool that hits rock bottom at 7.5' and has to pull the rod out :grin:
I've got $5 that the Hilti will make the top of the rod flush.
Of course, the rod may be 1" thick after that, or maybe S-shaped.
Added: By the way, if I got 7.5' driven and hit rock, I'd try to bend over the top foot.
Water:D
Sorry, can't resist!
Hey, it works.
Scoop about one shovel full of dirt. Pour in water. Push rod into ground working it up and down a bit.
I can usually push them in down to last foot or so (lose leverage about then) unless I hit a rock without much trouble. Hammer 'em the rest of the way.
No fancy tools needed. Silty clay soils in these parts.
A couple of advantages to this are it is quick and if you do hit a rock at 4 or 5' down you can easily pull the rod and move it over 6" or whatever. Good luck on pulling the rod if you pounded it in up to that point and you hit a large rock.
I am a big fan of the Erico driver. Roughly half the ground rods we drive are for temp services when no power is available so a hammer drill isn't practicle. If we are doing 100 10' rods for a ground ring then a hammer drill is the only option.
We use to use fence post driver until I watched an employee run a 5/8" ground rod right thru his hand. He lifted the driver up a little to high and when he came down will all his force the driver missed the ground rod and the rod went thru his hand. I use to have some good pictures of it, I'll have to look for them.
We bought the erico's for everyone the next day.
I guess we don't have to ask how you came up with your member name. :cool:
Just don't post it here with out a warning, some might not want to see it:cool:
I second the water, and then finish it off with a sledge if needed.
I have the fancy power tools too. I'll take a pint of water and race anyone here in IL.
I got this in an email today
Well, there are no rocks here:cool:
I have used an Estwing a couple times, but I usually stand on it the last foot or so.
I drove a 10' x 3/4" rod last Saturday for my Dad and all I used was one 12oz bottle of water:D