kwired
Electron manager
- NE Nebraska
For a start you maybe compare your load with transformer. Especially if there is higher levels of continuous loads involved.If I do an installation, I am obliged to do a load calc to determine if the service equipment is not overloaded.
But if I determine that the service equipment is correctly sized per article 220, at what point do I need to say anything to the POCO? Remember that the POCO has their own rules, and their installation is often undersized compared to the service equipment.
-Jon
When I am doing grain storage sites, other than commercial elevators, I mostly ignore loading and unloading equipment. The aeration fans are generally the major load, and on top of that when they run they often run 24/7 for days at a time. Loading/unloading equipment only runs 10-15 minutes at a time then may sit several hours before running again.
Bottom line is you kind of need to know the loading situation. Industrial plant - production loads may be fairly continuous, or they may be higher during one phase of operations than during others. Total connected load and what all runs at same time and for how long can be widely different.