When should you ask utility if there is enough power available?

Status
Not open for further replies.

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
And if things go sideways...

I can see the conference room now, during deposition:

<Plaintiff's counsel> "So, Mr. Tainted, let's discuss the load calculations you performed for this installation..."

I would just tell them I put an amp meter and used the worst case scenerio


Personally I don’t think it’s clear if the OP is regarding the load on the customer service equipment or the utility transformer. If it’s not about the service equipment and he just wants to tell the utility about the additional load then I don’t think he needs the full NEC calc. What his scope entails regarding the customer equipment may require a NEC load calc for the the electrical permit. Looks like a pretty easy case to use 12 month demand from the utility bills and add the new load.
How about both scenarios ?
 

Charged

Senior Member
Location
Ohio
Occupation
Electrical Designer
I would just tell them I put an amp meter and used the worst case scenerio



How about both scenarios ?
12 month demand will give you the basis for your NEC calc , that covers that, then you can see if you realistically have a problem with the utility transformer size , if you know the Kva.

I’ve gathered a bunch of data and Guidelines from various utilities so I can can guess the size they will select for the purposes of preliminary fault current calculations and planning purposes. One I have shows data they use like percentages of actual usage of design load. Regardless your past the point now and if you get a utility bill and your lucky enough to get good demand numbers then you should have a good idea if they have a problem you should notify them about.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
A commercial building owner we worked for blew up the transformer, the POCO sued them for 14k
Here its in the utilities TOS that you inform them of any changes in load over something like 5kw
Check the TOS
 

Charged

Senior Member
Location
Ohio
Occupation
Electrical Designer
A commercial building owner we worked for blew up the transformer, the POCO sued them for 14k
Here its in the utilities TOS that you inform them of any changes in load over something like 5kw
Check the TOS
This is good to know
 

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
A commercial building owner we worked for blew up the transformer, the POCO sued them for 14k
Here its in the utilities TOS that you inform them of any changes in load over something like 5kw
Check the TOS
Yea but what about NYC? What’s the kW cutoff to inform utilities?
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
A commercial building owner we worked for blew up the transformer, the POCO sued them for 14k
Here its in the utilities TOS that you inform them of any changes in load over something like 5kw
Check the TOS
It’s in ours also.
In all the others I’ve read too.
 
Does the AHJ accept that type of answer when you go to get a permit?
Only place I work where you need AIC/AFC to pull a permit is projects within the city of Seattle that require plan review. Even then they don't seem to look too close and the reviewer almost always just does a mark up for the field inspector to verify AIC ratings. As far as inspectors, yes I recently had one agree with me that AFC wasn't an issue just by looking at it. I have enough experience to have a pretty good idea when an inspector will be concerned about fault duty, and also to know when I need to do an exact calculation or not. There just isn't a black and white answer, just like the original question in this thread. Do I add load without doing a calc or contacting the power company? Yes all the time. Does that mean I NEVER get demand readings or contact the power company? No.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
So if I add a receptacle for a 1/30HP condensate pump to a 200 story building(over exaggerating), I would need to go through all the trouble of calculating the load of the entire building or do 220.87? That’s nuts. I don’t care what the code is, I’m not gonna explain the client to this and look like an idiot
Since that load is not required to be included in the original calculation, no new calculation is required.
 

NewtonLaw

Senior Member
I am making plans to utilize power from an existing switchboard. The load I would need is 15KVA.
When should you ask the utility if there is enough power available and if existing service is adequate for the load? Is it even required for low loads such as mine?
The answer depends. If this is an addition to your existing load and it will be a demand of 15 kVA, I.e., no diversity, then I suggest you let you local utility know of your intentions. Why? In PA and specially in PPL Electric Utility Corp. territory, three tariff rules filed with the PAPUC requires the customer inform them of any load increase. This is so the Utility can address the need for larger transformers and or secondary cables run from pole to pole for both load and voltage considerations. Example of a problem where the customer did not inform the Utility was, the customer replaced a 3 ton heat pump with a 5 ton unit and said nothing to the Utility. The customer experienced voltage drops during start that caused light flicker and general low voltage conditions for him. When he went to the Utility for an upgrade to his service he was told he had to pay for any changes to the transformer size or service conductor replacement since he was required to inform the Utility first, before he made the load addition. The PA Public Utility Commission supported the Utility since it was part of their tariff. It was not cheap. It would have cost him nothing if he had informed the Utility first.
 

Another C10

Electrical Contractor 1987 - present
Location
Southern Cal
Occupation
Electrician NEC 2020
I am making plans to utilize power from an existing switchboard
This note here basically sounds like the main will not be upgraded therefore Id say no worries on the load calcs. If you were adding a larger Main Breaker then yes the utilities should be informed normally through the city inspector after approval. that way the utilities can determine if the transformer they provide will still be sufficient.
 

kwired

Electron manager
Location
NE Nebraska
This note here basically sounds like the main will not be upgraded therefore Id say no worries on the load calcs. If you were adding a larger Main Breaker then yes the utilities should be informed normally through the city inspector after approval. that way the utilities can determine if the transformer they provide will still be sufficient.
Again, many services out there that don't have corresponding POCO transformer to supply the full service capacity, simply because the load isn't there.

I upgraded service in a school building a few years back when they installed new HVAC system. Went to a 1200 amp main @ 208/120. If full 1200 amps were needed the transformer likely would need to be about a 500 kVA. Based on previous demand plus however POCO figured the additional HVAC, they put in a 225 kVA - rated amps is about 625. I had a 600 amp feeder to the HVAC alone, though it was maybe a little oversized but definitely needed to be over 400 amps. The existing building load still on top of that but they figured 225 was what they needed. But for HVAC to draw full rated load it needed to be a really hot summer day, otherwise actual demand was going to be much lower most of the time. But one could easily add another ~600 amps of load to that service and not trip the main, yet the 225 kVA transformer maybe won't handle it so well.
 

Another C10

Electrical Contractor 1987 - present
Location
Southern Cal
Occupation
Electrician NEC 2020
But one could easily add another ~600 amps of load to that service and not trip the main, yet the 225 kVA transformer maybe won't handle it so well.
In that case I would think the liability would fall on the Utility for not accommodating a designed and approved main switch gear. My argument would be to the utility, hey.. I have the right to utilize 100% of my gears capacity or until it trips, why didn't the utility grid engineers prepare for my maximum consumption.
 
In that case I would think the liability would fall on the Utility for not accommodating a designed and approved main switch gear. My argument would be to the utility, hey.. I have the right to utilize 100% of my gears capacity or until it trips, why didn't the utility grid engineers prepare for my maximum consumption.
No, they don't care about your NEC service size, they generally go off the loads you told them at the initial design. They do sometimes have standards for how much they will "undersize" their equipment. For example, I just talked to Seattle city light about upgrading a 400A high leg (fed open delta) to 600. Service lateral is 500 AL, bank is not that big, maybe 125kva total. They said I could go up to 600 A service and they would not change anything.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
No, they don't care about your NEC service size, they generally go off the loads you told them at the initial design. They do sometimes have standards for how much they will "undersize" their equipment. For example, I just talked to Seattle city light about upgrading a 400A high leg (fed open delta) to 600. Service lateral is 500 AL, bank is not that big, maybe 125kva total. They said I could go up to 600 A service and they would not change anything.
For a bank that big we would definitely close the delta, unless the three phase portion happens to be under ~50kVA
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Only place I work where you need AIC/AFC to pull a permit is projects within the city of Seattle that require plan review. Even then they don't seem to look too close and the reviewer almost always just does a mark up for the field inspector to verify AIC ratings. As far as inspectors, yes I recently had one agree with me that AFC wasn't an issue just by looking at it. I have enough experience to have a pretty good idea when an inspector will be concerned about fault duty, and also to know when I need to do an exact calculation or not. There just isn't a black and white answer, just like the original question in this thread. Do I add load without doing a calc or contacting the power company? Yes all the time. Does that mean I NEVER get demand readings or contact the power company? No.
I've had when change of occupancy that required rewire and new loads that permitting and POCO wanted loads calculations. Also POCO wanted me to calculate loads and provide to them, then they'll determine whether they will change to meet my new loads on remodels.
 

kwired

Electron manager
Location
NE Nebraska
In that case I would think the liability would fall on the Utility for not accommodating a designed and approved main switch gear. My argument would be to the utility, hey.. I have the right to utilize 100% of my gears capacity or until it trips, why didn't the utility grid engineers prepare for my maximum consumption.
Many cases, particularly when you go over maybe the 100kVA range, you start to get into demand charges applying and need to be in more closer contact with POCO involving loading anyway. If you suddenly decide to add load without changing your billing agreements you will pay penalties for being over demand that will likely cost you more than had you informed them of the changes.

There is also minimum demand charges, fees you pay whether you use the energy or not, why subscribe for high usage if you are not going to use it? If your load changes then you talk to POCO about new minimum demand charge to better suit your load and they can at that time decide if they need to upgrade anything as well.
 