MAK
Senior Member
- Location
- Massachusetts-Boston
I was called out to a department store Friday evening to fix a delayed egress device on a fire exit door. When I arrived and opened up the device (Von Duprin Chexit) I found it was wired with cat3 (24awg solid).
The conductors were breaking off quite easily and I had suggested that it be rewired with 18awg stranded to prevent the problem from reoccurring. When I looked at the raceway (3/4" emt) I found thhn conductors with 120 vac in the same raceway as the LV wiring 24vdc (class 2). I told the customer I could not rerun the cable in the same raceway and that I would have to run a few pieces of emt to make it happen. Customer declined, and I patched it up as best I could.
The building is 13 years old. I presumed that all of their other doors were wired in the same manner. I also had found some of the fire alarm horn strobe wiring in the same raceway as well. This building was in Massachusetts.
My question is when was it allowed to have class 1 and class 2 wiring in the same raceway?
The conductors were breaking off quite easily and I had suggested that it be rewired with 18awg stranded to prevent the problem from reoccurring. When I looked at the raceway (3/4" emt) I found thhn conductors with 120 vac in the same raceway as the LV wiring 24vdc (class 2). I told the customer I could not rerun the cable in the same raceway and that I would have to run a few pieces of emt to make it happen. Customer declined, and I patched it up as best I could.
The building is 13 years old. I presumed that all of their other doors were wired in the same manner. I also had found some of the fire alarm horn strobe wiring in the same raceway as well. This building was in Massachusetts.
My question is when was it allowed to have class 1 and class 2 wiring in the same raceway?