250.56 Resistance of Rod, Pipe, and Plate Electrodes.
A single electrode consisting of a rod, pipe, or plate that does not have a resistance to ground of 25 ohms or less shall be augmented by one additional electrode of any of the types specified by 250.52(A)(4) through (A)(8). Where multiple rod, pipe, or plate electrodes are installed to meet the requirements of this section, they shall not be less than 1.8 m (6 ft) apart.
FPN: The paralleling efficiency of rods longer than 2.5 m (8 ft) is improved by spacing greater than 1.8 m (6 ft).
(2) Supplemental Electrode Required. A single rod, pipe, or plate electrode shall be supplemented by an additional electrode of a type specified in 250.52(A)(2) through (A)(8). The supplemental electrode shall be permitted to be bonded to one of the following:
(1) Rod, pipe, or plate electrode
(2) Grounding electrode conductor
(3) Grounded service-entrance conductor
(4) Nonflexible grounded service raceway
(5) Any grounded service enclosure
Exception: If a single rod, pipe, or plate grounding electrode has a resistance to earth of 25 ohms or less, the supplemental electrode shall not be required.
That was the confusing part (the use of the 2nd).I guess the use of just one rod in residential settings in this area of the world is adequate for the 25 ohm requirement or this was never paid much attention to.I have never seen a 2nd rod in use.This area being with in 50 miles of the coast may play a signifcant part.
thanks dick
They ought to just make it a rule that 2 grouind rods are required period, and forget the 25 ohm rule.
That rule got beat to death anyway.
If you drive 1 you always wonder is it actually 25 ohms or less? and if you drive 2 you wonder why you had to if 25 ohms or less was acceptable, so its a no win situation.
They need to take out the variable which is not a constant.
The changes in wording in 2011 now make it so that you must use 2 rods unless you want to go through the effort to prove the first one is low enough resistance to stand alone.
okay that would be the answer,,,,,,,,,2011 said
as a side note most all General Specificatiions from industrial plant engineering gurus stated that the grid systems would be interconnected driven rods to 25 ohms,,,,,this was normally met with rods 75 to 100 feet apart for the plant proper usually coastal,,,,,,,,,,,,,substations were different.
The engineering gurus can specify whatever they want and for their own reasons.
The NEC minimum is 25 or less for a single rod, if that is not met drive a second rod. If still not 25 or less NEC does not make you drive any more, but if engineers want 25 or less it will likely mean keep adding rods or making other modifications until 25 or less is met.
"You Must, Unless" is still a variable.
The resistance to earth changes daily, that's why I think they should do away with the 25 ohms or less rule but that JMHO.
Don't get me wrong. I agree with installing grounding electrodes. I just think there should be 2 required and the clause about the "Unless 1 will do it" should be removed.I think a little too much emphasis is put on grounding electrodes, but they are in the NEC and I must do what it says as a minimum.
IMO the requirement should be one rod regardless of anything else or any other GE's being present.
Roger