I will agree. 2 grounding rods,water line g.e.c. , Also bond h to c water pipes at water heater .They used 2" green pipe when I got city water.
Bonding the hot/cold water pipes at the water heater is NOT a grounding electrode requirement.
Bonding the interior metal water piping system is a 250.104 requirement - it is about clearing faults.
Bonding the hot/cold water pipes together at the water heater is something done by electricians who don't know folks now have indoor showers/tubs along with their indoor toilets.