peter d
- New England
So far nobody has identified the most obvious problem - General Electric breakers.
Correct, until the ATS transfers
or there is a power blip from the POCO.
At that point the inrush just happens to be more than when it was manually switched on- and thus trips. Inrush magnitude is never identical.
Again how does that, right or wrong, apply to my situation? :huh:
The transformers are energized, they stay energized for months at a time and then all of sudden it is off.
Given the fact there are no in rush loads other than the transformers themselves I am not understanding where you are heading.
How?
The transformers are not cycling unless the ATS is cycling and I can find no evidence for that.
How?
I checked for that, does not seem to be the case.
In a building with literally dozens of transformers and similar breakers all over the building yet only this one is tripping?
Seems like a reach.
So this power company 'blip' you speak of are you talking 'lights out' for a second or a slow brown out or a very quick short dip?
Unless you are talking 'lights out' the transformers stay energized correct?
Well at this point it looks like there is either lack of sufficient information ....
:thumbsup:
I agree and if I learn more I will share it.
I do appreciate the help from everyone, if we could all walk the job it could be fun.![]()
Would your customer allow you to post a walk-through video?
I do not dispute that, but back then breakers tended to have a very high magnetic trip rating, assuming they even did in the first place. A good chunk of manufactures were thermal only. Over the years many arguments in the industry from fires to arc flash to magnetic force have resulted in breakers with substantially lower magnetic trip levels and even lower starting levels for those breaker which have adjustable settings.
For at least 40 years now there has not been a major manufacturer of 'thermal only' breakers sold for general feeder and branch circuit protection.
To my knowledge the industry un-official standard for thermal magnetic breaker is roughly 5-10X for pickup with most adjustable breaker in the 2-12X range.
Yes, the actual operating and clearing speed of molded case breakers, is such that selective coordination can only be determined by physical tests.
Seems like a reach.
Nah, I can't stand your accent.![]()
I know there are WAY better sources, but this makes mention of inrush current varying in magnitude depending on where a transformer is switched on in the voltage sine wave. The concern is great enough that some POCOs will do "point on wave switching" with large transformers which in a nut shell makes sure the circuit breaker contacts close at the exact point in the sine wave that produces low inrush.
https://www.ijsr.net/archive/v5i2/NOV161123.pdf
Is anyone talking about slapping recorders on everything and waiting to see what happens the next time?
However, I just want to point out you might still be correct. 500 feet @ 1/0, 7.5kva, no motor loads and a 70amp breaker... now that I crunch the numbers (albeit roughly) it might be a reach.