Except to get to this condition the connections must be physically changed from the first example.
To me I see the absolute is; the actual physical arrangement makes a difference.
Whether we have the voltages in
X1->X2/X3->X4 or
X1/X2->X3/X4 or
X3->X4/X1->X2 or
X4->X3/X2->X1 or
X4/X3->X2/X1 or
X2->X1/X4->X3 or
does not change the fact that the X1->X2 voltage is in phase with the X3->X4 voltage and the fact that the X1->X2 voltage is opposite in phase to the X3->X4 voltage.
Change the actual connections get different results.
What connections have to be changed to make both Van and Vnb have a 0? difference as well as Van and Vbn have a 180? difference? Why do you think we have to change the connections inside the transformer?
I'll requote you so you don't have to scroll up.
That demonstrates that both voltages exist, not that we have to change the internal transformer connections to use those voltages.
Your graphic, in post 847 shows two sources on the left side of a center-tapped transformer feeding a single winding on the right hand side, which is also listed as a source. This is not a standard 120/240V connection.
The two generators serve to show that we can have two 180? physically displaced voltages supplying a load. From the right side, we have the standard center-tapped transformer fed by a 2-wire primary. The left side source (made up of the 180? labeled generator-supplied voltages) is paralleled with the right side source (made up of voltages from a standard single-phase transformer).
This is not a standard 120/240V connection. But let us ignore that minor detail.
Nothing to ignore. The transformer on the right is a standard single-phase transformer fed from a single-phase source coming from the right. That is about as standard as it gets.
You show a current as flowing out of node A at the same time one is flowing into node B effectively we could call these currents Ia and Ib. If your currents and your voltages are in-phase with each other (based on the resistive load) why is Ib not flowing out?
Because of my whole point that the directions are relative. Look at the generator on the left. Using the normal reference, we can see that the currents are indeed flowing in those directions. It is also a physical fact that the two generators are identical except that one is physically rotated 180? relative to the other. V
A and V
B do indeed have a 180? displacement.
By the way the current paths you show are exactly what I would predict using industry standard transformer connections of into X1 and out X4.
That is a good thing since I do not disagree with that. It is the assignment of the positive direction that we disagree on. As my graphic shows, that is arbitrary and either way is valid and both agree with the physical reality.
But they are not what David posted in #156 when he was solving a previous question
Did not really follow that line of conversation in detail. As I recall, I wasn't paying much attention that argument but I thought it was an argument about "the sum of currents into a node equals zero" vs "the sum of currents entering a node equals the sum of currents leaving a node" so pretty much skimmed over it. Did I miss something?