If anyone is interested, I have a theory about when and why a 4-wire feed is required, and when it's optional. In other words, "why."
For the typical 3-wire utility supply, whose neutral carries current, the premises neutral voltage (relative to the system ground and/or the earth itself) may rise a few volts, but it does so as a whole.
In other words, adequate bonding minimizes potential differences, or gradients, between various surfaces that we consider grounded, such as EGC's and GEC's, enclosures, and the plumbing syetem.
Note that beyond the main bonding jumper, the neutral, the grounded conductor, is treated as a non-grounded conductor, other than OCP. And, relative to our premises ground, it's prudent to think of it as such.
In a detached building, there's a whole new premises with its own interior system with neutral current, which means that structure's neutral may also rise above the originating supply's neutral voltage a bit.
As in the main house, we don't really care if the system ground has a little voltage above zero, as long as it rises as a whole. The presence of another conductive pathway from the main house changes all that.
A cable-TV coax, for example, has a shield that could act as a ground reference to the neutral and either develop shock voltage between them, or force neutral current on the shield. Neither are desireable conditions.
Now, with a 4-wire feeder to the separate structure, the neutral voltage can rise a bit if it likes, without creating a voltage difference between the main house's MBJ-point and this strcuture's grounding system.
Well, I don't know where I was really headed with this, except that's how I see it, and maybe thinking about it helps with the theory hidden behind the requirements. Hope it was informative.